PROFIBUS problem using GE Fanuc 90-30

pavel47

Member
Join Date
Jul 2005
Location
Lausanne
Posts
20
[font=verdana, arial, helvetica]Hello

I have problems with PROFIBUS.
I tried with 2 configuration (with same result):

1. CPU 364 + IC693PBM200 Profibus Master Module
2. CPU 366 (with integrated Profibus Master)

When I download and RUN my program, PROFIBUS is in BUS FAULT state.

The same PROFIBUS network I tested with Siemens.

With Siemens it was Ok...

Thank you in advance.

Pavel.
[/font]
 
Did you load all of the correct GSD files into the CPU?
Each node, or slave should have one.
Until you do this (or configure them all manually) the GE Fanuc Profibus master will not know the bus and will show a fault.
 
Thanks

The problem is resolved.
The error was in WAGO I/O configuration.
One sould put the name of root WAGO module in the list of attached I/O modules.
 

Similar Topics

I try adding another node to the card is as SST PFB3 VME is a woodhead brand card. It not working property, the configuration that works has 9...
Replies
3
Views
4,314
Dear All, I have a KUKA Palletizer machines having Iconics Genesis SCADA installed on its PC. It remained closed for about 7 to 8 years. We are...
Replies
0
Views
957
Hello guys, I have problems with the Porfibus communication to my regulator Siemens Sipart DR 21and my PLC rockwell 1756-L161. So, for the...
Replies
8
Views
2,094
Hey guys, it's been a little while. I'm having a problem that I can't seem to figure out. I'm using a Helmholz FLEXtra® multiRepeater. 6 way. I...
Replies
22
Views
5,375
Hello to all, I have a strange problem with establishing the communication between WinCC HMI station and the rest of Profibus network. We have...
Replies
14
Views
3,860
Back
Top Bottom