HSCE 1746 Question

Acme

Member
Join Date
Nov 2005
Location
Chicago
Posts
2
I have read the manual and I still am a little bit confused about where the HSCE writes to about amount of pulses it has counted?

Thank You
Zach
 
The accumulated count shows up as an input word. their symbol is "I:e.1" the 'e' should be replaced by the slot number that the module is inserted in. Thus, if it's in slot 2 the address of the accumulated ccount is I:2.1
 

Similar Topics