RSlinx Enterprise RSView DF1 communication to PanelView Plus

pcola

Member
Join Date
Nov 2005
Location
pensacola, fl
Posts
22
I have tried to transfer a program to a PV+1250 via DF1 or DH485, but it will not connect. RSLinx will autoconfig and show the panelview (as a computer). I close out RSLinx and Enterprise Linx will not find it. Any suggestions?
 
Linx Enterprise and Linx "classic" will not happily share a com. port; have a quick search on the AB knowledgebase for an appnote on this.
 
RSlinx and RS Enterprise

I shut down the RSLinx so that there was no conflict. I originally tried it with both, but saw the conflict error. Then I tried only the Enterprise, and it will not find it. I appreciate you responding.
 
The technote is G45350891, it's note quite as easy as just closing RSLinx, Enterprise must start up first. This may not be the end of your problems but give it a shot. You're using a 2711 cn13/14 cable and have set the PV+ serial baud etc. yes? (Sorry if this is sounds like I'm teaching you to suck eggs but........)
 

Similar Topics

When I start up FactoryTalk View Studio, I get an error box labeled RSLinx Enterprise. It says: "An internal error has occurred. You must close...
Replies
1
Views
9,065
Hi All, Looking for some clarity regards the relatively recent rebranding of RSLinx Classic. From what I can make out from the RA website and...
Replies
9
Views
2,350
Besides a $3,000 license to purchase a RsLinx Gateway License for every remote computer network that I work on. Is there another way to get to a...
Replies
4
Views
2,686
Hi, I'm running FTView v9 on a VM machine. Host win 10 64 bit, virtual win 7 pro. I've come to configure communication on this project (1st...
Replies
2
Views
2,161
Good day, Does anyone know if the device shortcuts can be backed up, if they are stored in a SQL-Database?
Replies
3
Views
2,015
Back
Top Bottom