Siemens TP170B

girevik

Member
Join Date
Nov 2005
Location
rus
Posts
179
Hello,

there is a touch panel, siemens tp-170b, connected to the simatic S7-300 (314) PLC... it has been working just a well, but now TP shows error 190100, type - 2, number - 1.

According to the manual, that error means that TP's program is corrupted or so...

There is another similar TP that work well with that PLC, so I have a tend to think that the problem is in the TP, but I believe it's not dead and just program have to be re-downloaded... is that right? And Can I upload program from one TP and download it to another(I just have not that project on PC, so the only one way to get the program is to upload from another TP)? what should I use? ProTool? WinCC?


anyone ever have meet such error? any thoughts?


thanks!
 
If you can get to the Windows control panel then you can easily backup the TP170 to a standard Compact Flash card.

If there is no button or function in the application to access the Control Panel, then cycle power to the TP and wait for a start menu to appear. Be quick to select "Control panel" before the runtime application starts automatically.
Then use the Backup/Restore utility that you will find amongst the utilities in Control Panel.
The backup will be a complete image of the panel Win CE, DLLs, protool RT file etc.
 
That way worked very well! thanks again..

Now I'm wondering if there is a way to do something similar with S7-314 CPU's, is it possible to copy program from one PLC to another by using external flash card or so...? can I download program from external flash card to the PLC?

thanks
 
If the S7-314 is a recent model then there MUST be an MMC card in it for it to run.
To exchange the CPU, you just move the MMC card from the old to the new CPU.

Older S7-314 models have a combination of battery and MC card program backup. You can recognize the MMC card in that it is much smaller than the older MC card type.
 
the cpu made in 2002, the memory card slot seems to be pretty big, little bit larger than compactflash cards....

this cpu was working well without MC, but then internal program were erased... so now it can work with MC (there is a similar program on it) only...

so i'm wondering if there is a way to download the program from MC to CPU, so it will work without MC again? I have tried to find it in a S7-300 manual, but have found nothing, may be because it's for newest cpu mostly...

thanks
 

Similar Topics

Dear Friends, i have a problem with a Siemens TP170B. I can't transfer my project by MPI of my PC. Error Message in attach. I can't resolve the...
Replies
6
Views
3,913
Greetings i need to do programming / configuration for a new Siemens TP170B what connection cable do i need ? if it is attached to Siemens...
Replies
0
Views
2,415
Hi Im using Compact Logix L32E PLC and Siemens TP170B HMI using Win cc flexible.How to communicate between this two? There is no Ethernet port...
Replies
2
Views
3,374
Hello, I have a service engineer on site, and he is struggling with a touch panel. The touch pointer is way off where he is pressing the touch...
Replies
4
Views
4,513
Hi, we are using Siemens S700 PLCs with add-on modules and use the TP170B screen (and the replacement TP177B). A service engineer with thick...
Replies
3
Views
5,376
Back
Top Bottom