Dear Experts

Above mentioned drawing has been taken from one of AB power supplies manuals. In this way we may get 20A redundant 24V dc.

But our requirement is to get 40 A redundant 24V dc. Is it possible that if we connect both |”GND” & both “+24V” & make a common bus bar?

Would we be able to get 40 A redundant 24 DC on that common bus bar?





(please consult attached word Doc for more details)

Is above topology Ok

Please advice

Best Regards

Muhammad Asim Khan
 
No. Connecting them simply in parallel will not result in a redundant supply. That will do the opposite, and will probably take both down if one dies due to an output problem.

Get two 40A supplies, connect the commons together, and connect the +24 lines together through 40A (or greater) Diodes. You will probably need to heat-sink the diode's. A 24VDC relay on each power supply output (before the diodes) can be used to detect if one supply has failed.

This is the circuitry that is generally inside of the manufacturered 'Redundant Power Supply Interface Modules'.
 

Similar Topics

Hi guy, Appreciate if you guys can give me some info/manufacturer which has a power supplies with the following spec; Input: 2x 240V AC (one...
Replies
4
Views
2,571
I am not new to PLCs but new to old PLCs. My company just got this machine in from an unknown company using the 1747-L20A SLC 500. My question...
Replies
6
Views
1,897
I wana communicate with AB PLC 1747 L20A, I want to now that how can it communicate with that processor I have RS 232 in my Laptop and also what...
Replies
1
Views
1,616
Hi I have a 1747-L20A Fixed PLC and I want to know what cable I can use to program it. I am also looking for the cable pinout so I can make it...
Replies
8
Views
2,996
I have a 1747-L-20A. The inputs have the common labeled as common and are tied to gether internally. The inputs themselves have 2 diodes opposed...
Replies
3
Views
2,463
Back
Top Bottom