Can we replace SLC P7 supply with P1 for following 13 slot configration

asim_rana

Member
Join Date
May 2005
Posts
50
Dear Experts

We are using following SLC configuration

Chassis size 13 slot
Slot-0 1747-L531E
Slot-1 Other (Prosoft Communication Module)
Slot-2 1746-IV16
Slot-3 1746-IV16
Slot-4 1746-IV08
Slot-5 1746-OW16
Slot-6 1746-OW16
Slot-7 1746-OW16
Slot-8 1746-OW08
Slot-9 1746-NI04
Remaing slots are empty

Initially we were using 1746-P7 .It had become faulty now we have 1746-P1 in stock can we use it instead of 1746-P7

Best Regards
Muhammad Asim Khan
 
In RS500, if you go to the I/O configuration, and then click on power supply, you will see that both the P1 and P7 are too small for the amount/type of I/O that you have, a P4 is the best replacement.
 