I use RSlogix 5k.
Can someone give me a code snippet on how to use PIDE?
Currently i use regular PID block and i want to convert it
to PIDE.
I need it for auto tuning.

Thanks
 
Hi

in addition,where do i place the PID structure?
If i change the SP in the program where should i place
it.

How do i call this PID routine from a routine in a continous
taks.

many thanks
 
Place the PIDE instruction in either a FB or ST routine under a periodic tast. PIDE cannot be used in or called from the continuous task. You may scope the PIDE tag globally to the controller or locally to only the program under the periodic task. You can enable/disable the PIDE from a routine in the continuous task if you globally scope the PIDE tag by setting/clearing the EN bit.
 
There are a lot of vestigial parameters on the PIDE instruction. Some of the parameters that I actually use are:

CVROCLimit
CVManLimiting
ControlAction
and the PV,CV, SP limits or scaling

You will need to disable CVManlimiting and put the PIDE into ProgMan mode in order to use the Logix5000 autotune. Alternatively, you may want to look into RSLoop Optimzer, it can tune without upsetting your process.

Here's a screen shot of our typical implementation. Note that we do not use HandHand, OperHand, OperOperAutoMan or any of the many other control modes. If manual modes are required, our logic takes care of this on its own.

AK
 
Hi And thanks for the reply.

Where should i place the PID predefined data type
which i place in the regular PID routine as the first parameter?

I need the .SO and .SWM parameters

Thanks
 
Confusion alert!. The PID datatype applies to the Standard PID block that is the CLX analogy of the one used in the SLC/PLC family. The parameters you mention .SO and .SWM appear to relate to that function, not the PIDE function which is unique to the CLX and is only implemented in Function Block.
 

Similar Topics

Greetings ... someone sent me a request for some student handsouts that I developed ... turns out that I had this hosted on my business website...
Replies
0
Views
131
Have a logix controller and I'm using the PIDE block for the autotuner. I've got the hang of doing it for direct control things like pressure...
Replies
21
Views
1,765
Studio 5000 version 34. Have error on PIDE CVFaulted (Status1.2), Control variable (CV) health bad. No more information online or in...
Replies
3
Views
966
Hi everyone, I am trying to add a control loop to my HMI interface however I keep getting the following issue, any idea why this would happen?
Replies
8
Views
1,613
We have a routine that we trigger with a JSR every 10 seconds that has PIDE instructions. This resides in a Periodic task that triggers every...
Replies
6
Views
922
Back
Top Bottom