Need help to choose an Allen Bradley system

Cryogen

Member
Join Date
Oct 2005
Location
NH
Posts
151
Our customer is requesting an Allen Bradley system (preferably a PLC) for one analog 4-20mA input and three analog 4-20mA output. There will be one PID(level control) on the system.

Can you guys give any recommendations? I know its AB, but there should be a cheaper solution considering there is nothing complicated here..

I appreciate any help!!
 
You can get into a ML1200 with the Analog IO for around $500.00

A CompactLogix with the IO will run just over a grand. The ML1200 PID is a good PID, but the compactlogix has a much more advanced PID instruction available.
 
Whilst I do not agree with Alaric that the ML1200 PID instruction is good it does work and it is (relatively) cheap. The problem is that scaling the 4-20mA for the PID loop is ridiculously complicated. You should make sure that you read the help files and all of the available tech notes before you code your loop(s).
 
Thanks for all your help. I think I will go with Micrologix 1200 and use two 1762-IF2OF2s modules. The current version of RSlogix I have is 5.50. Is this fine for me to use?

Can I consider ML1000 Analog? Is there a good price difference between ML1000 and ML1200?

I have never programmed PID in Allen Bradley. For someone to start, how much time will it take to program one PID loop?

Thanks again for your help!!
 
I avoid the ML-1000 for any analog work. Math functions and scaling are limited, and you only have one comm port. I'm not sure if it as PID. For what you are doing, the 1200 is a more economical choice long term.
 
ML1200 should be a good balance of price and functionality..

Now, the customer wants the ability to change the setpoint and PID. This application will not have an operator interface, they would have to connect a laptop to the PLC.

I want to let them change the setpoints, PID etc but i do not want them to add more code.. or be able to download new program. Is this possible for me to do? Can I password protect say a subroutine or something?​
 
If the 1100 has enough I/O it may be a better choice. It has an LCD display that you can give them the ability to change setpoints with. Also, it allows online programming, which the 1200 does not.

Darren
 
If I go with ML1100, I may have to update my RSlogix500 right?
I assume the display can be password protected?
 
Last edited:
Go with the M1100.

This allows online changes to the logic, whereas the rest of the Micrologix family does not. Nothing more frustrating than waiting till production is over at 2:00am to download logic changes or updates to an application.

Ian
 

Similar Topics

Hi friends; I have PLC of Ge Funac 90-30 series with 8 i/o chasis. In old system the high speed counter module is installed IC693APU300 but before...
Replies
3
Views
1,844
I'm fairly new to Rockwell software, I've had some basic training in the past but nothing too advanced. My company and I use Reliable products for...
Replies
11
Views
340
Hi all, I am having issues accessing my Cimplicity software - the site code changed after re-install and I am no longer able to attain a new key...
Replies
10
Views
166
Good day all! Can someone help me with the procedure to update Beijers E700 firmware? The Panel I am working on is firmware 2.04v and I would...
Replies
1
Views
70
Back
Top Bottom