Long story made short- Purchased a hydraulic power unit for an automated manufacturing machine we built. This unit is controlled with an AB-MicroLogix 1000 (AC-Relay out) PLC. The unit did not come with Isolation relays in its control panel. The PLC’s AC Relay outputs directly power 6 hyd-valve solenoids, that fire about 20 times per min each. These solenoids state the following:
78VA
268VA inrush.
120volt.
Now the problem, we are 2 days out of warranty on the PLC (which 1/3 of which was in the power units builders shop during spec-ing and construction). We have “Burnt Out” 3 of its outputs. By that I mean that the PLC is telling its relay to break, but they are “sticking” on and continue to actuate the coils inappropriately. I can tap the side of the PLC with the butt end of a screwdriver and it will unlatch the output. We are also having a problem with failing prox-sensors and cylinder position sensors. These sensors came with the Neumatics brand cylinders that we installed on our machine. After failing, we are replacing them with Turk brand (which seems to be holding up better).
So far my investigation on our difficulties have lead me to believe that we need to install isolation relays that the PLC will actuate in order to free the relay output from the inrush (make or break) current. That is no big deal. Here is where I’m confused. After contacting numerous manufactures for advise as to which of the three inductive protection devices I should install on the coils and to what values I should choose, not one could enlighten me. My interest is to not only shunt the transient voltage that is present in “our” control panel, but to protect the sensitive electronic devices from the inrush (make or break) currents that I believe is also present. The machine's main control panel was built wrong to begin with. The builder ran control voltage wiring along with/parallel to/ and in the same pan-duit as the higher voltage conductors also present in the panel. Can someone afford a little education on TVS’s, MOV’s, and RC Snubbers, or have I missed the point entirely?
Thanks- barry!
78VA
268VA inrush.
120volt.
Now the problem, we are 2 days out of warranty on the PLC (which 1/3 of which was in the power units builders shop during spec-ing and construction). We have “Burnt Out” 3 of its outputs. By that I mean that the PLC is telling its relay to break, but they are “sticking” on and continue to actuate the coils inappropriately. I can tap the side of the PLC with the butt end of a screwdriver and it will unlatch the output. We are also having a problem with failing prox-sensors and cylinder position sensors. These sensors came with the Neumatics brand cylinders that we installed on our machine. After failing, we are replacing them with Turk brand (which seems to be holding up better).
So far my investigation on our difficulties have lead me to believe that we need to install isolation relays that the PLC will actuate in order to free the relay output from the inrush (make or break) current. That is no big deal. Here is where I’m confused. After contacting numerous manufactures for advise as to which of the three inductive protection devices I should install on the coils and to what values I should choose, not one could enlighten me. My interest is to not only shunt the transient voltage that is present in “our” control panel, but to protect the sensitive electronic devices from the inrush (make or break) currents that I believe is also present. The machine's main control panel was built wrong to begin with. The builder ran control voltage wiring along with/parallel to/ and in the same pan-duit as the higher voltage conductors also present in the panel. Can someone afford a little education on TVS’s, MOV’s, and RC Snubbers, or have I missed the point entirely?
Thanks- barry!