Electrical Safety
Just knowing about 480 isn't enough. Locking it out can also lead to a false belief that you can't get hurt. Take changing the rotation on a motor. Most will do it at the local disconnect (yes I put them on all motors). If its off and locked out, then the top will be hot. Yes I know everyone knows it's hot and stays away, but NFPA 70E doesn't just allow it. There is still the potential. To fully comply with NFPA 70E, you would have to lock it out at the MCC and then after wearing the proper PPE and verifying it is not energized, then you could change it at the disconnect without all the silly gear.
I think what most people are assuming is that you have to wear the blast suit to change a light bulb. These rules aren't designed to be scary, they are designed to protect you in the extremely unlikely event that something bad happens. The proper method is to do an arc flash and fault current study on everything you have in your plant. I know it's expensive and I've been doing it this way for 40 years who are NFPA to come in and tell me something different, but it is truly necessary. I've worked at many plants that have no idea of the magnitude of the fault current at their gear and I can't believe it. How can you properly design a panel without knowing this. All 30 Amp breakers are not the same (look up AIC). IF this is done, then the rest of the calculations aren't that bad, but they should still be done.
You might also be surprised that if your company (or you) deside to do it correctly instead of the simplified method (which is way overkill in most cases), you might be plesantly surprised. I just the plant that I work at and it is huge compared to most (1.8 million SF and over 600 different machines with a power bill in the 10's of millions per year). After looking at the simplified method, we spent the money for SKM Powertools. That made everything very easy. Since we have to huge substations to supply our plant, the available fault current is pretty large.
After making some adjustments to the trip settings of the breakers, most of the equipment at our plant is level 0 or -1 (yes, negative 1). That means that the workers are protected at cotton clothing. Every piece of equipment is marked with the amount of energy available, the category, the approach distance for flash hazard (many are less than 4 inches) and the required PPE. Even my MCCs are still cat 0 so no suits are required.
I've heard a lot of moans and groans and I can't believe its, but when it comes down to it, the employer is responsible for you if you get hurt, they will be fined by OSHA if you get hurt, they will still pay workmans comp if you get hurt and many will feel bad if you get hurt. It's in their best interest to implement these rules and they need to do it.
If anyone needs any information about all this, we are almost fully compliant here, I will be glad to help and explain or show you anything.