please explain k,p bus -UR1/UR2, ER1/ER2,CR2

tomkens

Member
Join Date
Dec 2003
Location
manchester
Posts
21
I would be glad if someone tells me diffrence between P Bus and K bus.how about UR1/UR2, ER1/ER2,CR2
is it usefull to know buses for configuration of s7-400?
 
tomkens

Lets see if I can help you out here with my limited knowledge of S7 400 racks.

The two types of backplane bus available are the P and K bus, from what I remember the P bus is for I/O updates and the K bus for communications updates. The P bus is the slowest and is also the only bus available on the S7 300 range.

The racks mentioned are as follows:-

UR1 - Universal rack, 18 slots wide, has both P and K bus
UR2 - Another universal rack, 9 slots wide, again has both P and K bus
ER1 - Expansion rack, 18 slots wide, only P bus available
ER2 - Expansion rack, 9 slots wide, only P bus available
CR2 - central rack, 18 slots wide but split into two segments, this can be used for operating two independent S7 400's, each with their own I/O etc, but both PLC's can communicate with each other via the K bus in the backplane.

There is one other rack that you didn't ask about, that is the CR3 rack, CR3 is very similar to the CR2 rack, but is usually used with S7 400H PLC's, it can also be used as an expansion rack.

tomkens said:
is it usefull to know buses for configuration of s7-400

I don't think so.

Hope this helps you a little.

Paul
 

Similar Topics

Just for readers in the US, when I write 'gas' I mean it as a state of matter, not shorthand for gasoline :-) I don't understand the logic of a...
Replies
39
Views
11,170
Good Morning , Could you please explain to me what a S:FS is , what the purpose of it is and why would it be used in a rung. Thanks so much.
Replies
4
Views
1,716
Good Afternoon , We have a number of Kinetix 6000 Servo Drives and motors. I'm trying to understand these a little ( really alot ) better...
Replies
16
Views
6,347
Good Afternoon , We have a new machine from Italy , and for some reason , the servo actual positions quit updating on the HMI. I looked at...
Replies
6
Views
1,713
Hello, I started my new job at a factory and I found that when I opened the PLC cabinet there are "ABB contactors" that are connected to the PLC...
Replies
9
Views
3,326
Back
Top Bottom