Siemens S5-100U question

dalem

Member
Join Date
Sep 2005
Location
NE Wisconsin
Posts
104
I looked at Siemens site, but could not find S5 manuals to answer my question. I recently picked up an S5-100U PLC with rack and cards for spare parts for an induction welder in house. (I had one input module that may have had issues.)

Anyway, all components in this spare unit are identical to those in the machine, except for the CPU. In the machine is a 6ES5 102-8MA02. In this spare is a 6ES5 100-8MA02. After that part number, there's the 6 boxes with some of them XX out. The 100 unit has 1,2&3 XXX out. On the 102 unit in the machine, only 1&2 are XX out.

Questions:
What's the difference between the 100&102unit?

What's with the XX out boxes?

Thanks in advance,
Dale
 
100/102/103

RAM 1024/2048/10240 statments
Ex,time 0.07/0.007/0.0016 ms
Timers 16/32/128
Counters 16/32/128
BIO 128/256/256 max
FB240... no/yes/more Integrated FB/OB (math etc.)

...8MA02 with manual 6ES5 998-OUB22
...8MA22 without manual
 
Last edited:
From the 1998 ST50 catalog, the 102 is a lot more capable.
Memory: 2Kb vs 4kB
Execution time: 70ms vs 7ms
Counters: 16 vs 32
Timers: 16 vs 32
Arithmetic functions: +,- vs +,-,x,:

IO and communications is limited on the 100 as well.

Hopefully this will help you

Adrian
 
The X'd boxes indicate the version of that particular module. Typically, once the X'd number reaches 9 the last digit of the part number will be incremented and the X goes back into a box "1".
 
Thanks a bunch.

As I see it, there's a chance the 100 would work in place of the 102, but far greater chance it will not. I have no way to check the programming on the Eprom, so I'll just hang on to the 100 thinking posiibly work if needed, but most likely not.

Thanks again.
 

Similar Topics

Hello! Can someone tell my if I need a programmer of some kind to transfer the program from my PC to the PLC, or can i do this wiht the cable...
Replies
2
Views
2,145
dear All, i am working on the step5 of Siemens. after successful upload program and going online but RLO data is not updating. In Tset>Status...
Replies
6
Views
2,061
Hi, I have several 100U CPU's with either broken Run/Stop/Copy switches or broken off/on switchs. Does anyone have a source for replacement...
Replies
0
Views
1,657
Hi all, I need to interface a Siemens S5-100U PLC part number 5ES5 103-8MA03 onto an Ethernet network. Are there any protocol converters...
Replies
2
Views
1,701
We have an old system controlled by a siemens plc s5 with order no. 6es5 102-8ma02 we want use for this system operating panel siemens op25 but so...
Replies
3
Views
2,878
Back
Top Bottom