Hi Folks,

Is that any "2 wire" to "5 wire" converter for modbus ?

Cause i have 5 Terminal for modbus module and the field instruments

have only 2 wire ( modbus )..


Regards
 
At Plc Module I Have 5 Terminal .. Tx+, Tx-, Rx+, Rx- And Ground..

But My Instrument Only Have 2 Wire ..

So How Should I Do The Terminaltion?

Regards
 
The "2 wire" is created by tying Tx+ to RX+ as 1 wire and Tx- to RX- as the other wire. Look up the PLC's requirement for termination resistors. Then try this hookup with the closest "2 wire" instrument. If it works, add on another always moving the other set of termination resistors to the far end of the line. Of course like any other network the Modbus devices will have to be assigned distinct addresses.

Be careful about major differences in the grounding. You may wish to use isolation between the PLC module and the line.
 
You probably have RS485. Just connecting the wires, as suggested by Bernie, may not always work. Some drivers are not universal.

My favorite RS485 technical literature comes from Robust Data Comm.
 
As noted by Jim Dungar the method behind the hardware is not always the same. Though the protocol, Modbus, is defined, its method of implementation could be taking advantage of the seperated transmit and recieve channels which the 4 wire allows. If so it may not like the 2 wire hookup. That is why I suggested trying it just on one unit. I assume you don't have any information on the PLC side requiring one or the other else you wouldn't have to ask.
 
The instrument you are using, reads from the PLC module or writes to the PLC module? maybe a manual written for the instrument might have stated what it needs and what it does. Sometimes you just need Tx+ and Tx-, or Rx+ and Rx-, or as Bern said, TRx+ and TRx- (jump the positive connections together and same goes for the negatives). :D

regards
Sherine T.
 
If you jumper the 'like' rx and tx lines on the 4-wire device, the issues you're going to need to watch for are (i) does the 4-wire device turn off its transmitter when not sending? and (ii) does it turn off its receiver when it is sending? If it's a 4-wire master device, it may not meet either of these conditions...
 
repeater

I had the same problem some time ago.

You need in RS485 (two wires) to RS422 (4 w) repeater.
I use I-7510a.
 
It's worth trying it as a 2 wire, half duplex link by jumpering as advised above.

Some companies, like Honeywell, provide all 4 terminals, but only implement half duplex (2 wire), and state as much.

Dan
 

Similar Topics

I'm trying to control a device via MODBUS RTU and the ModbusRtuMasterV2_PcCOM in Twincat 3. I've configured a device with the right com port and...
Replies
7
Views
221
I am trying to figure out some communication specifics for a Modbus RTU network that I will be integrating with and could use some help to make...
Replies
9
Views
2,080
I'm getting no response from a device I'm trying to communicate to with a Beckhoff IPC. I'm not sure why it's not working. Attached are pictures...
Replies
0
Views
627
HI guys: I am attaching several diagram from several sources, it seems to be that there is no such a wiring standard for modbus RS485 RTU. In some...
Replies
24
Views
4,519
So I'm working on an old project I did several years ago. It has 12 nodes on a modbus RTU network. I'm going back for an expansion. I'm going to...
Replies
5
Views
1,895
Back
Top Bottom