I have a couple PowerFlex700 hooked up to 1747-SDN card and everytime the PLC cycle power or when the program is downloaded, the drives gives a DeviceNet Port 5 fault code of 75 and I would have to go to the drive and reset the fault before I can continue using it. Anyway to clear this fault automatically when communication with DeviceNet is restored?
 
Idle and Fault behavior are programmable on the PF700.

The 20-COMM-D interface in the PowerFlex drives can be configured to react separately to Communications Idle and Communications Fault events.

What's happening in your case is that the 1747-SDN goes into "idle" mode when you download a new program to the controller, and if you cycle power to the PLC obviously communications stops totally, resulting in a communications fault from the drive's persepective.

The exact parameter number depends on your version of the drive, but look in RSNetworx for DeviceNet in the DeviceNet parameter group for these parameters:

Comm Flt Action
Idle Flt Action


The default value is the most conservative action; fault the drive when either event occurs. I usually set my drives to Stop when an Idle or Comms Fault occurs. That way I don't have to manually or programmatically reset the fault.

An alternative is to have the controller automatically reset the fault over the DeviceNet link. Bit 02 of the command word is the Reset Faults bit.
 

Similar Topics

Hi, I have a previously used PowerFlex 700 with DeviceNet and I want to use it to run a 20HP motor powering a water line at constant pressure...
Replies
3
Views
1,357
Hi friends. I am working on PF700, and drive is showing at speed no faults but when I am hooking up the motor, motor doesnt starts and only shows...
Replies
8
Views
1,724
I want to connect my PLC 5/40 to my Powerflex 700 trough RIO remote I/O. I am connected to the PLC trough a 1. How is the wiring in the Remote...
Replies
0
Views
1,273
We have a Power Flex 700 VFD installed which in turn gives power supply to 55 kw motor. Once the VFD tripped due to over heating of vfd. We...
Replies
7
Views
10,102
Hello, I used the powerflex 700 driver,the driver via 20-comm-e with PLC (1769-L32E) communication,I use the rslogix5000 software config the...
Replies
9
Views
2,952
Back
Top Bottom