Hi All,

I have to find out how much 17x1,5kW and 3x2,2kW inverters use in inrush.

The 1,5kW inverter have needs a power supply capacity of 4,5 kVA and the 2,2kW inverter needs 5,5kVA.

It is 3phase and I have 400V between the phases

Total is 93kVA and gives me 134Amps.
But how do I calculate the inrush current.
With inverters there are a very little inruch current but I do not know the formula of calculating it.

Can someone please help me on that.

Thank you

Dariusch
 
Gerry M said:
I would check with the drive manufacturer.

Yes I would do that, but the are closed until to tomorrow and I would like to calculate the total currunt for the switchboard tonight.
 
Using a drive you should not have inrush current, you will either use it in volt/hertz or scaler, each should have linear output current. And, with the drives being capacitive in nature they also help correct power factor.
 
So when for example the 1,5kW inverter is rated 4,5kVA it would be 6,5A = inrush?But I was thinking that the inverter would have some inrush, because the always requeres som fuses that are bigger than the Ie.
That would be because of some Ist.
 
Because inverter have caps on their internal DC buss, I gotta believe there will be some inrush current. Question is, how much? Did you check the mfg's website for any online documents?
 
Any info I could get was the power supply regurement in kVA. But no info on inrush.

Think I have to wait til tommorow.

Thanks anyway

Dariusch
 
When i spec in drives I still use the 125% overload to spec in breaker sizes just as a rule of thumb. I have never seen any inrush current on a drive, as a q&a , I always use a fluke 43b power quality analyzer it measure inrush. As for the precharge caps, when power is applied to caps they act as a short ciruit until they reach full charge,so i doubt that they will act as inrush.
 
I guess it depends on how you define inrush. If the bus caps initially act as a short circuit, and draw current accordingly, where does this current come from?

Most of the AC drives I have come across have a precharge circuit built in to the power circuit. This limits the maximum available current level supplied to the bus until the bus voltage is near its maximum level. I have heard numbers like 95% of full charge tossed around. After that point full current is allowed. This is why it is a bad idea to frequently cycle power to an AC drive. you will cook the precharge circuit.

A precharge circuit may be why nswu1 isn't seeing any trouble with inrush current to the drive. Another possibility is that the trip curve on his circuit breaker is such that the short term inrush doesn't cause a problem.

Keith
 
nswu1 said:
...As for the precharge caps, when power is applied to caps they act as a short ciruit until they reach full charge,so i doubt that they will act as inrush.

I define that as inrush. Be it inductive or capacitive.
 
An inverter will have a very small idle current and a specified full load current. The input supply fuses etc are based on that full load value.

When you power up the drive, even tho it is idling, the current will go up to charge the DC bus caps over the normal idling level. It will not go so high as to exceed the full load input current.

As a result, if you size your supply per the instruction manual for full load current, you will not see any higher levels than that for power-up inrush.

The bottom line to this is that there is no higher inrush current to deal with.
 
One word of caution. Many drives that may not have much inrush during normal cycling will have tremendous inrush on power up. Some as high as 2 to 3 times the drive rating. While this won't matter for you running calculations, it will matter depending on what type of circuit protection you use. Fused it will not be a problem. But some circuit breakers will react too quick and trip on power up. I have seen this happen on an application with about 20 drives. Power the system up and every breaker would trip. After continuously turning the breakers on till the capacitors were charged, the breakers would stay on.
 
Dariusch you are correct in your question. These drive will have an inrush current that would blow the fuses IF you size them to the nominal motor specs.

In some plants I work, the electrician have the knowledge to size the fuses for the motor nameplate.

For instance, if the motor nominal current is 4 Amps, they will install a 5 Amps fuse (time delay of course) but when they do this on a system that has Inverters we get a call for the fuses sometimes melt.

We have had arguments with many. Then they will accept installing fuses rated for the nominal current of the Inverter. Same problem, the inrush kills them, specially when the guy switches the main disconnect ON and Off a few time in a short period.

In the Inverter manual there is always a recommended fuse size and this takes into effect the inrush of this particular brand.


I've tested the inrush a few times and its really short, not like a motor starting. We had gotten 22 Amps for less than 0.5 second on a 1.5Kw drive.

To size the main breaker for this is out of my ball park. Sorry. But its a genbuine good question.

We usually install the fuses to protect the wires not the drive. So for a 14 guage wire we install 15A.

Not the best but accepted by inspectors :(
 

Similar Topics

Hi everyone, This is my first time posting, so please forgive any omissions or mistakes. I am attempting to control the velocity of a stepper...
Replies
18
Views
954
Good morning, I have a question. I don't know much about ST yet I would like to calculate the average number of products per hour. how do I do...
Replies
22
Views
2,941
Can someone help me with this? I'm no good at SCL - virtually everything I've done so far has been ladder logic. The return value from the...
Replies
13
Views
1,101
I want to calculate the energy consumed from instantaneous power. Can this be done using the TOT block with timebase set to Hour?
Replies
2
Views
684
Hi everyone, I have to calculate the length in millimeters of a glass that enters a transport (I don't know the speed yet) through a barrier...
Replies
15
Views
3,456
Back
Top Bottom