Pinout info
Pin no.:
Code
Meaning
Input / output
1
NC
Pin 1 is not connected
-
2
M24 EXT
M24 EXT return line (GND) of the 24V power supply.
The current load from an external user connected between P24 EXT and M24 EXT must not exceed a maximum of 150mA.
Output
3
LTG_B
Signal line B of the MPI module
Input / output
4
RTS_AS
RTS_AS, control signal for Receive data flow. The signal is "1" active when the directly connected AS sends.
Input
5
M5 EXT
M5 EXT return line (GND) of the 5V power supply. The current load from an external consumer connected between P5EXT and M5EXT must not be greater than 90 mA.
Output
6
P5 EXT
P5 EXT power supply (+5 V) of the 5V power supply. The current load from an external consumer connected between P5EXT and M5EXT must not be greater than 90 mA.
Output
7
P24 EXT
P24 EXT power supply (+24 V) of the 24V power supply. The current load from an external user connected between P24 EXT and M24 EXT must not exceed a maximum of 150mA.
Output
8
LTG_A
Signal line A of the MPI module
Input / output
9
RTS_PG
RTS output signal of the MPI module. The signal is "1" when the PG/PLC sends.
Output
Shield
Connector housing
You can find this (as well as more useful info) on SIMATIC Support pages (www4.ad.siemens.de), Entry ID 3001321
Best regards,
Sven