parky said:
if using 3 wire input & 2 wire rtd connect one side of 2 wire rtd to the 3rd connection
You're right, and I've used this trick many times. You should always check how much error is going to be induced, though, by jumpering at the input card.
For example, on a recent job in Idaho I had a 3-wire input and a 2-wire RTD on an alarm unit. I jumpered as you described. There was approximately 500 ft. of #18 AWG between the input and the RTD location (250 ft. each direction). That added about 3.25 Ohms to the resistance. (#18 AWG is 6.5 Ohms/thousand feet at 77 Ā°F.)
I was using a Pt 100 Ohm RTD, 0.00385 Ohm/Ohm/Ā°C alpha, and my alarm trip point was 240Ā°F or 121 Ā°C. This corresponds to 146.5 Ohms RTD resistance. The 3.25 Ohm error meant that when my input measured 121 Ā°C the actual resistance at the RTD was 143.2 Ohms, and the actual temperature monitored was only 115 Ā°C or 239Ā°F.
In my case the error was not significant, and was on the safe side, and I could tweak my trip point if I wanted to. So, the jumpering worked just fine. It had the added benefit of confusing the heck out of the guy from GE, who wanted the contractor to rip out all of the RTD wiring and was fairly obnoxious about it!
On the other hand, in some applications a 10Ā°F error is going to be a problem.
The moral of this long story is that it is OK to work around differences between the preferred and the actual equipment. Just make sure you know the impact of the work-a-round and account for it in the control.