quick update (short on time) ... plcnovel called me by phone earlier this afternoon ... if I understand correctly, his analog input module and his analog output module are both “configurable” types ... if so, I recommended that he set both of these modules for their “Scaled for PID” configuration ...
specifically, I !think! that he should be able to take the 4-to-20mA analog input from the field device into the analog input module and have the module itself scale the data from 0-to-16383 and feed it directly into the PV of the PID ...
also I !think! that he should be able to take the 0-to-16383 CV data from the PID and feed it directly into the analog output module and obtain a 4-to-20mA signal for his field device (valve, etc.) ...
from my end of the pipe, I have ZERO field experience in setting up the type of application/machinery that plcnovel is working on ... personally, I’m fairly ok on the Allen-Bradley PID instruction, but if anyone has some nuts-and-bolts experience on the specific type of machinery in question here, please take a stab at this ...
my basic “next step” recommendation is to temporarily disable the PID rung ... then (carefully! - and safely!) manually enter values into the PID’s CV address ... a value of “0” should result in a 4mA output signal to the field device ... a value of “16383” should result in a 20mA output signal to the field device ...
while this operation is going on, monitor the PID’s PV address ... when the input field device is putting out a 4mA signal, the PV address should contain the value “0” ... when the input field device is putting out a 20mA signal, the PV address should contain the value “16383” ...
personally, I always start out a “PID-controlled” project this way ... specifically, I make CERTAIN that the field signals are properly scaled (from 0 to 16383) at the PV and CV locations BEFORE the PID is ever activated ...
reality check: most industrial equipment won’t let you safely force it to the minimum and maximum values of its operational limits ... so you might have to use a “process calibrator” to simulate and nail down the 4-to-20mA signals ... but at least do SOMETHING to make sure that the PV and CV signals are properly scaled and addressed before trying to configure and tune the PID loop ...
note to plcnovel ... you REALLY need to post your complete .RSS file ... the folks on the forum can give you MUCH better help if they know exactly what hardware you’re using ... and how it is configured ... case in point: your “configurable” type analog modules may either complicate or simplify your problems - depending on how you have them configured ... it’s hard for us to give detailed advice when we don’t have detailed information to work from ... personally I will be teaching non-stop for the next two weeks and will have VERY little time to help ... I wish you the best of luck ...