Rockwell CLX >< SCADA communication problem

obsen

Member
Join Date
May 2006
Location
Cph.
Posts
8
Hej
Suddenly my communication between my SCADA and my 2 CLX is not working properly.
I use RSLinx gateway for the communication, but suddenly (after working fine for 1½ years) some of my OPC groups are not updated anymore (10 out of 28). I can see in RSLinx, that data is requested, but nothing happens.

Any ideas?

Yours

Ulrik Obsen
NHL-Automation
Denmark
 
In RSLinx, for each DH+ station in the "RSWho" browse, you should be able to right-click and select "Station Diagnostics".

These diagnostic counters may include information about the nodes that RSLinx is connecting to.

Can you use RSLinx for any other functions involving these controllers on the DH+ network ?
 
Thanks Ken


Should have described the situation bit more:

I use Ethernet to communicate with the 2 CLX.
I can go online on the PLC's with my Logix5k, no problem.

I have checked various statistiscs and the only spot, where I can find something is in the OPC group diagnostics:

The groups that are not updated in my SCADA has a large number of Subscription packets and a large number of Updates before sent.

Can anybody make something of that?

Thanks

Ulrik Obsen
 
You did not mention what SCADA you are using, I guess is RSview32 or Rsview SE or Rsview ME, if the case is the first one check your topics on the rslinx classic they are probably corrupt, and your scada look thru them.

If rsview se or me then check device shotcuts on rslinx enterprise and verify they are pointing to the right side.

widelto
 
Im not using RSView, im using IGSS (Danish developed SCADA).

I have found the problem. The OPC server in RSLinx has sent some data to SCADA timestamped May 20th. The SCADA system does a verification of the timestamp, and since something is clearly wrong, data is discharged.

Why RSLinx has timestamped wrong I dont know. The Clock in the CLX is correct.

I have turned of varification af the timestamp, and now things seem to work.
 

Similar Topics

I have several Avery scale units and they are configured as Generic Ethernet modules, and I am actually reading the data fine for the weight...
Replies
2
Views
400
Dear Automation guys, Im quite new to Rockwell. I have to do the migration of logic from PLC-5/40 to CLX L71 CPU. So far: - I have done exports...
Replies
5
Views
2,668
I am considering switching some of our future machine builds from the CLX L16 to Micro 850. It's about half the price with our current pricing...
Replies
3
Views
3,444
Hello fellow members, Has anybody interfaced Toshiva VFD TOSVERT-300MVi with Rockwell's ControlLogix? Any examples? Regards, --Rahul.
Replies
1
Views
3,559
Hello, recently I saw a graphic from any Rockwell App, I cant identify which one is. Attached a SS. Its used to see dashboard from datapoints and...
Replies
2
Views
56
Back
Top Bottom