Hello
i am getting an "F012" "I too Low" fault on a masterdrive. is there any Siemens gurus out there that can help me off the top of their head?

scott
 
You might see this if a CT went out. Change P100 to a 1- this is
V/HZ mode. P60 must be set to a 5 first- then change P100 to a 1, put P60 back to a 1.
I want to make sure your motor will at least run.
Let me know want happens.
 
I am not familiar with the parameter details in Siemens drives but, usually when you get a "current too low" fault, you would expect to find an underload detection parameter set in the drive. Underload is intended for use in pumps and similar applications where a lack of load on the motor means that the pump is running dry and seal failure is emminent. This type of fault protection is not used on very many other applications.

I'd take a quick look around the drive parameters and see if your drive has this feature turned on. If it's not needed, turn it off.
 

Similar Topics

hi, i want to work as a siemens micro master drive using two analog input choosable, digital input 2 is disenable analog input one select...
Replies
1
Views
2,045
I have a word in some DB which I want to load to AR1 and use as a pointer. In order to do this I need to write L DBxy.DBW xy SLD 3 LAR1 I...
Replies
3
Views
533
Hi Complete newcomer to S7 so go easy on me... Siemens S7: What cable do I need to connect S7-1200 PLC to HMI? The touch screen is one of these...
Replies
14
Views
2,595
Hello all! I have a PN Coupler connecting two PLCs, one on X1 and one on X2 and am able to transfer data using the IN and OUT configuration...
Replies
1
Views
1,185
Hi i have just been asked to upload a plc program from 1511-1 pn it has v15 firmware 2.6 the machine oem doesnt support the machine i got...
Replies
11
Views
2,630
Back
Top Bottom