Modbus RTU

vintoms

Member
Join Date
Jun 2002
Posts
4
Hi,
Can Modbus RTU communicate over RS232 COMM port @ 64 kbps? I'm trying to communicate two control logix MCM modules (MVI)

cheers
 
The MCM is capable of RS232 baud rates up to 115,200. Standard selectable baud rates are 110, 300, 600, 1200, 2400, 4800, 9600, 19,200, 38,400, 57,600, and 115,200. 64 Kbaud would not be a valid selection for the MCM Module and, in 35 years in this business, I can't say I have seen a device communicating at that baud rate.
 