I am looking at adding 2 compact block IO modules to an existing RIO network. This is no problem to do. I was going to mount the IO on 2 sets of tooling. Is it posible to unplug those nodes from the network when a tool change is done?
 
Not knowing what PLC you are using, nobody here can say for sure, but I do know that some PLC's allow you to set up remote nodes so that communications loss will not cause a shutdown. Others won't have this option. Look for a setting that lets you dictate how the system will handle a node communications loss.

Steve
 
The PLC is a SLC 503. In the users manual for the scanner card it tells you how to use the M0 and M1 files. There is a Device Inhibit Control which you can inhibit selected nodes from the program but it also says that over time the nodes will return to their last state. I don't know if this will work properly.
 
The main challenge is that RIO is a daisy-chain network that requires termination resistors on the end of the cable.

If you put one of the termination resistors on the removable machine, you will have to connect a replacement resistor to the network when you unplug the removable equipment.

There is also a chance that the whole network will fault when you unplug the removable equipment, because one termination resistor will be missing.

RIO is fairly forgiving, but only a physical test will find out for sure.


If this is a system that shuts down while you are removing gear, then it's no problem. If the RIO network has to keep running even though you've unhooked the end of it... maybe a problem.
 

Similar Topics

So I'm pretty new around here but I come looking for advice or suggestions to research. Im the plant electrician/SCADA guy for a warer department...
Replies
4
Views
88
See the screenshot of EIP tag list. We are trying to read in a digital input that is hard-wired. It is shown here as I31.1. I believe we cannot...
Replies
7
Views
282
Hello Dear users, I am writing about a problem that has been bothering me for a few days, i.e. I am trying to establish remote access to the Allen...
Replies
0
Views
88
Hello All, I need the ability to remotely reboot a Red Lion CR3000 HMI. Due to some graphics issues when the database is updated the HMI must be...
Replies
4
Views
218
I have to provide remote access and control to a touch screen. I was thinking about using Weintek and the Weincloud. Does anyone know if this is...
Replies
11
Views
596
Back
Top Bottom