My customer has a powder tablet pressing machine from a company not longer in business. I was asked to replace the feedback from the load cell from the original controllers to an analog PLC card from AD 260CPU.
Question:
Based on the specs I have for this load cell, does anyone know what component I need between the Load Cell and the analog PLC?
Specs:
GAUGE EXCITATION VOLTAGE: 10.00 VDC
CHANNEL NUMBER: 2
PRESS MOUNTED GAUGE CALIBRATION: 2.8329 mV/V
@ CALIBRATED LOAD: 6.96 TONS
MAX. GAUGE OUTPUT:28.3 mVDC.
FIXED GAIN RESISTOR: 1.18K OHMS.
MAX.PRESS LOAD: 20.00
RATIO=1: 0.3478
Thanks for your help