hi, everybody,

i have to communicate modicon quantum 424 PLC with PCS7 (Scada Side) through modbus TCP/IP..
Quantum 424 has two ports Modbus & ModbusPlus,,,

Can i use the same ModbusPlus port for this communication or have to use separate ethernet module...

i also wants to know which softwares i need ( i have proworx).to to establish modbus TCP/IP communications between 424 & PCS7..

Thanks in advance.......
Regards,
Khalid
 
There are several mutually exclusive communications ports available on the Quantum CPU and various expansion cards. The ports on the 424 CPU are serial ports, not Ethernet. You will either need an Ethernet to serial converter (ProSoft and others make them) or else add an Ethernet expansion card like the NOE 511 00.

I'm not sure what a PCS7 is (Siemens maybe?) so I can't help you there.
 
The Quantum can initiate communications using the MSTR function in 984 Ladder logic (your ProWORX software). This is easy to implement using the Modbus Plus port or by adding an NOE module.

The most typical method is to have the Quantum respond to communications requests generated by your PCS7. In this case there is no programming needed in the Quantum and you could even use the Modbus serial port if speed is not an issue.

As Tom mentioned, you will have to get an ethernet bridge device. Each bridge device will have its own set up procedure.
 
Thanks for your replies,


it means then i only need 140NOE77110 (which is modbus over TCP/IP)in quantum rack. and there is no need of serial to ethernet converter.
ist there any special software to program 140NOE77110. or only by ProWorx.

Regards,
Khalid
 

Similar Topics

I want to what i need for communication with Modicon Quantum 424. What sort of cable is required? any special card? I am using windows 2000...
Replies
4
Views
3,003
Hello All, Was hoping I could get a little help with Modicon ladder logic. This is the first time I have seen Modicon logic and currently trying...
Replies
6
Views
239
Hi There, I have a Modicon Quantum PLC, there is a alarm on display "noConfig" its happened after power failure, I have gone through manuals...
Replies
3
Views
638
Hey guys. Mostly new to this stuff so I apologize if I'm not following proper format. I have 3 working CPU133 /3s. There is a desktop with a...
Replies
2
Views
878
When i read the specification of 140CPU43412A i observe that as remembered in specification 1. Local i/o : Maximum i/p and o/p words are 64 in...
Replies
0
Views
487
Back
Top Bottom