Modicon quantum communications

khalid_inayat

Member
Join Date
May 2006
Location
Jeddah
Posts
20
i m using Modicon Quantum 424 PLc and try to connect my PC with modbus port but i m getting an error.. Bad Response Checksum Error 120 wat does it means.
when i monitor this through modbus tester code is recieving from PLC but with error.i made the cable according to the drawing and using the right setttings (RTU 9600, Even, Data bits-8,stopbit-1,flowcontrol -none) but still i m getting the same error.
what is the cause of this problem.

Regards,
khalid
 
Are you getting this error continuously or intermittently? Do you ever get good communications? It may be the cable has a loose connection, or you may have a noise problem, or you may have different parameters for parity and such.

A little more detail, please.
 
yes i m getting the same reply again and again .........

01 illegal function.....
modbus LED is blinking...........,
i checked all the connections of cable

PLC PC
1 5
2 3
3 2
5 5
4 6
6 4
7-8jumpered on both the sides.i have some doubts regarding cable.
can u verify......
 

Similar Topics

Hi, I am using Citect (redundant Servers) and Modicon Quantum (Hotstandby) and using NOE ethernet module for communication. THe updation speeds at...
Replies
4
Views
5,266
Hello All, Was hoping I could get a little help with Modicon ladder logic. This is the first time I have seen Modicon logic and currently trying...
Replies
6
Views
257
Hi There, I have a Modicon Quantum PLC, there is a alarm on display "noConfig" its happened after power failure, I have gone through manuals...
Replies
3
Views
650
When i read the specification of 140CPU43412A i observe that as remembered in specification 1. Local i/o : Maximum i/p and o/p words are 64 in...
Replies
0
Views
494
Main rack contained power supply 140cps52400 and 140cpu43412A and RIO HEAD 140CRP93100 in addition to another I/o cards . Another remote rack...
Replies
8
Views
1,859
Back
Top Bottom