OPC Quick Client- a bad quality

Hello blackslipper;

You are not connected properly, or have not configured the OPC link correctly.

See the following table [from the OPC toolbox help files]:
Bad Quality Substatus Strings

Value

Substatus String

Description

0

Non-Specific

The value is bad but no specific reason is known.

1

Configuration Error

There is some server-specific problem with the configuration. For example, the item in question is deleted from the running server configuration.

2

Not Connected

The input is required to be logically connected to something, but is not connected. This quality may reflect that no value is available at this time, possibly because the data source has not yet provided one.

3

Device Failure

A device failure has been detected.

4

Sensor Failure

A sensor failure has been detected.

5

Last Known Value

Communication between the device and the server has failed. However, the last known value is available. Note that the age of the last known value can be determined from the TimeStamp property.

6

Comm Failure

Communication between the device and server has failed. There is no last known value available.

7

Out of Service

The Active state of the item or group containing the item is set to off. This quality is also used to indicate that the item is not being updated by the server for some reason.


hope this helps,
Daniel chartier
 

Similar Topics

Hi, I'm communicating my RSView32 with a Yokogawa FA-M3 PLC on Ethernet. I've a demo version of DeviceXplore FA-M3 OPC Server, RSView32 works...
Replies
2
Views
3,813
Unregistered
U
I am running CCW 13 trying to upload to a micro 820 vers.12 I get an output message OPC server is unable to load project controller. Please help!
Replies
5
Views
221
I know nothing about simaticnet OPC server. I do know Kepware. I would only ever scale raw to engineering in the PLC, but it is possible to scale...
Replies
5
Views
215
If anyone has a crack for IBH OPC Server, please send it to: [email protected] Urgently. Thanks in advance!
Replies
1
Views
126
Folks, I have a client with an old ABB Advant / MOD300 system (v14.4). Around y2k I installed the ABB Industrial IT MOD300 OPC Server 1.1/2...
Replies
1
Views
175
Back
Top Bottom