Hello

-How many I/Os /digital and analog/ could I connect to a PCS 7 Box. Is there a limmitation?
-As I inderstood I can display 250 variables only on the Scada / it does not matter if they are a bit, byte, word or dword /. Is that right?
-When it is better to choose a PCS7 than a PLC system?

Regards
 
Last edited:
1. 16 kbyte I, 16 kbyte 0. But really less: 8 kbyte IO on DP, 2 kbyte 0 on MPI/DP.
2. Yes, but 250 is the quantity of external variables (in PLC memory) which are connected to SCADA. Quantity of internal variables is limited to 8k. If you want more, you must either use dword and row tags, or to buy the power pack.
3. PCS7 is more expensive. But all depends from IO quantity. PCS7 has own libraries - 1-st advantage; after creating object in Step7 it automatically is linked with WinCC - 2-nd advantage. If you have more than 500 IO, you can think about PCS7.
 
Hello Gromit:
This is from a PCS7 presentation document for version 6.0.
PCS7_tags.jpg


We've regularly more than 2500 tags in each PCS7 "boxes" in our last project.
PCS7 is an integrated plant-wide distributed control system; it is Siemens' "DCS on PLCs". It uses high-end S7-400 CPUs and hardware, Profibus-DP for field connectiosn, Industrial Ethernet for plant wide communications (between CPUs and PCs). It requires the use of special engineering languages CFC/SFC, not included in standard programming packages like Step 7 Basis or Professional. For these programming environments, there is a large library of functions, including digital and analog signal treatment, math, communications, PIDs... There are SCL-based techniques to create user-defined fuctions that can be included in the library.
The OS (operating stations) stations are based on Siemens' WinCC, but with extended functionalities, such as linkage with the program functions. Say you create a function for motors in your program; you will expect input(Start, stop, Speed reference) and output (Status, Alarms, Speed feedback) parameters; you will also associate the function with a graphic symbol from the image library in WinCC. When you compile the program, it will generate code for the PLC, as expected; but it will also generate a screen in WinCC, with the selected symbol and alarm displays, for example.
basically, treat PCS7 as a DCS. Use it where a DCS is required, for plant-wide operations, multiple local loops control, and distinct areas to be covered.
The last project we used PCS7 was for an aluminium plant, covering processes as dfferent as smelters, anode-forming and cooking, transport of ingots and anodes, silo monitoring and communications.
For a single (or a few number of) machine, it is a huge investment.
Hope this helps,
Daniel Chartier
 
Last edited:

Similar Topics

Hi, What is the easiest way to create a Watchdog between 2pcs S7-1200 over Ethernet?
Replies
4
Views
1,501
I am experimenting with a very simple program for testing purposes and not getting any movement from the servo motor. The attached program...
Replies
6
Views
1,782
I dont have connection with this panel. Please help me. Can anybody worked for whis panel? I try connect the rs232-usb cable on the foto, but...
Replies
0
Views
1,140
410E with TP900 different IP range I have a PCS 7 410E REDUNDANCY CPU connected to the TP900 panel, from CPU side the X8 port address is...
Replies
0
Views
944
Hi, I have a question about Siemens ET200M series modules. These will be used in a remote IO panel. In this panel will be a dual redundant Siemens...
Replies
2
Views
1,322
Back
Top Bottom