I have been trying to find out if I can connect +24VDC Output to terminal 2 (start control) of a powerflex40 drive directly from a flex-i/o module or will I run into trouble with leakage current? I have seen others use a relay and don't know why.
 
Never dealt with the Powerflex 40, but in a lot of cases, the drive has it's own 24 volt power supply, and your output will have a different 24 volt supply, an interposing relay is used to isolate the two power supplies from each other.
 
The poweflex drives have an option for you to use external supply - you need to remove the jumper between term 1 and 11.
 
Remove that jumper when terminal 1 is used as a stop input. I've never read that you can use an external voltage to control this drive.
 
I have used an external supply in the past - it shows you in the manual but know where can I find out if a PLC output can be wired directly to the run signal.
 
There are (2) switches on the drive I/O board; one is for selecting 0-10V/0-20mA for the analog output, the other is labeled "SNK"/"SRC". Place this switch to "SNK" if you wnat to use an external 24 vdc supply.
 
I know the SNK switch needs to be set and I know you can remove the jumper and put +24VDC on term 1, -24VDC on Term 4 and for FWD control, put +24VDC on term 2. But I always see everyone either using a relay or an isolated ouput relay card to control term 2 - does anyone know any reason for doing it this way and not just using a standard output from a 24VDC output mod such as 1794-OB16 (with all 24VDC from same source)?
 
aisystems said:
I know the SNK switch needs to be set and I know you can remove the jumper and put +24VDC on term 1, -24VDC on Term 4 and for FWD control, put +24VDC on term 2. But I always see everyone either using a relay or an isolated ouput relay card to control term 2 - does anyone know any reason for doing it this way and not just using a standard output from a 24VDC output mod such as 1794-OB16 (with all 24VDC from same source)?

The Drive creates it's own 24VDC power supply.
Using a relay allows you to avoid tying the 2 24Vdc power supplies together.
 
Usually, the digital inputs are very high impedance and will not load your PLC outputs noticeably.

If you want to test the leakage current, simply connect a milliamp meter between the drives's +24VDC terminal and the digital input. I would expect it to be less than 10ma.
 
The powerFlex 40 User's manual on page 1-17 shows the hook-up using an externally supplied 24VDC switch. It mentions that each input draws 6ma. Is that a sufficient minimum for the FlexLogix module?
 
The 1794-OB16 spec manual states on-state current minimum is 1mA per channel (per channel I believe to be per output). Does it sound like it will work then?
 
I have done what your are talking about, feeding a PLC output straight int othe drive. Just make sure the commons are the same or tied together.
Regard Alan Case
 

Similar Topics

I have an issue with Power Flex 525 during running processing, the VFD stopped suddenly while the PLC and VFD connection ok, VFD does not have any...
Replies
1
Views
134
We are looking into installing a well water pump (480vac, 25hp, 40FLA) with a PowerFlex 755 VFD. The challenge is that the well is located about...
Replies
13
Views
4,720
We have a used piece of water filtration equipment. Long story short, 2 motors/pumps that are currently on contactors. Pump1 needs to be sent...
Replies
41
Views
20,656
I want to run a VFD through plc signals....how many inputs signals to need to run vfd?i.e, START,STOP,RUN FORWRD & REVERSE....
Replies
10
Views
4,085
Hello, first of all let me state for the record that I'm not a tech of any kind, I have limited experience with industrial automation devices, so...
Replies
3
Views
114
Back
Top Bottom