gas,
You need to establish a min run time for each pump. This will establish the resoulution in time you need to track. If it's possable that a pump might only run for 20-45 seconds, then you need to track the accumulated time in seconds. If any given pump will run for a min of 60 seconds then you can track in minutes.
The issue here is that if you dont track using the approperate resolution, the actual run time vs. the accumulated tracked time will eventually become so far off, it will be usless.
Additionally there is a basic maintence problem with the theroy of rotating load so all the equipment wears at the same rate, and to play catch up on the wear rate from one to the others. The problem is that the eqipment will eventally get to the point where all the pumps will fail, or require servicing all at/or near the same time, possably taking the entire process down, and leaving no or inadaquate backup to continue with min. production requirements.
In a critical operation it's usually the best practice to intentionally cause a group of pumps to wear at a greater rate then others. When group A is down for servicing, Group B will take the predomonent load, etc.. Spreading out the service factors over time, thus limiting the risk of a total shutdown.
Simply put, some types of production equipment should not be assumulated with rotating the tires on your car. If the equipment was installed with 10 pumps, but designed to run full production with 8 pumps in service, you dont want three or more pumps to require servicing at the same time, thus interupting production capabilities.
So depending on the applicatiion, you might want to sequence your pumps so you always start with Pump 1, then Pump 2 etc.. as the demand calls for. Pump 1 should require serviceing first, so then the sequence would start with Pump 2, then 3...then after pump 1 is back on line it would be the last pump in the sequence. When pump 2 would fail, be serviced and placed back on line, then it would be the last.. and so on. This would spread out the service intrevals between pumps so they wont all fail at or near the same time.