Hello All
I have a comms problem with rsview. First of all i lost my working files for my program and had to re-write them as laptop went down.

Having writen new screens tested comms paths with runtime on laptop everything seemed fine. But when i downloaded to touchscreen
error failed to find comms path fortunaly i could used the old comms path and it works okay. The problem is when they switch the machine power off they have to go into screen and set comms path.

Any help People
 
If it is ethernet, ensure that under terminal settings on the config screen that Use DHCP is set to NO. Also make sure that under RSLinx enterprise, that there are no other communications links defined that are not used but the PV+. When you download to the PV+, check on replace communications.

See if any of this helps and good luck

Marc
 

Similar Topics

Posted this to Reddit with little success, so I figured I would share it here as well. Very new to PLCs, but figured I would give it a shot to...
Replies
0
Views
44
Hello fellow wirenuts, I am looking to find the P.B. touch indicator option on version 13.00 and failing. It has been a year or so since I last...
Replies
4
Views
124
Hey all, i have a panelview screen (image attached), with 4 items on it. Program 1, Program 2, ...3, ...4. The PLC i am using is a compactlogix...
Replies
5
Views
137
Hello All! Ok, we got a Work cell from a Integrator that is sending saved scanning data from the PLC to HMI (Panel View Plus) when I look at this...
Replies
3
Views
64
Hi everyone, i have a compact logic 1769-L18 PLC and I'm using FTalk View ME for the display. I wanted to do some visualization on Grafana. At...
Replies
1
Views
75
Back
Top Bottom