omron c200h cup31 problem

jugenzhu1963

Member
Join Date
Jun 2006
Location
toronto
Posts
72
hi,
I got a problem with c200h plc which is on an old machine. i can not communicate with it using "work online". i try auto online and got a message "modem port has been selected. do you wish to continue? after press "yes" i got the upload but the plc type is CQM1 CPU11 and the programme contain lots of errors. i use cx-programmer 4.01. i don't know what's the problem. anybody can help out?

thanks a lot
 
Hello jugenzhu1963,

I assume that there is an LK201 "Host Link Adaptor" fitted to the PLC rack.
On the front of this unit are 4 switches.
Sw3 sets the baud rate, Sw4 sets the Data Bits and Parity etc.
Sw3 set to 5 means 9600 baud. (6 = 19200 baud).
Sw4 set to 1 means 7 Data bits, Even Parity, 2 Stop bits.
Set the network settings (Sysmac Way - Driver tab)in CX-Programmer to match the unit switches, and you should be able to go online normally.

Hope this helps.
 
try this.mostly i make mistake on this,
check you serial port setting in the plc and com port for serial used by your computer,,it should be the same..
 

Similar Topics

I have a sysmac omron plc C200H CPU01,only the power led is ON,using CX-ONE programmer software, and connecting to the plc via Host link LK202-V1...
Replies
2
Views
701
In order to upgrade a control unit, we need to backup program of an omron C200H CPU01 with host link LK202-V1 that has RS422 D9 Connector. Please...
Replies
2
Views
623
The logic seemed to convert nicely, and I had to make changes to the addresses for my AD and DA and 32-point input cards. The current problem is...
Replies
2
Views
1,034
I am trying to display some scaled analog input values on a C-more Micro terminal, from an older C200H Omron PLC. The addresses appear to simply...
Replies
5
Views
2,153
I have a customer with the Omron C200H that occasionally will start flashing the alarm light and the machine stops. They say they can power down...
Replies
10
Views
2,925
Back
Top Bottom