Need help. I am tring to create a graph. time verses an analog input from a pressure transducer. I need to look at a 20millisec window recieving an update every 1millisec. I also need to display this graph on a 1400e panelveiw I am using rslogix. thanks in advance
LW
 
You may be asking for more than your hardware can deliver. The 1771 analog input modules don't refresh their data as fast as you need, and your PLC scan will likely be an order of magnitude slower.

Depending on the model number, a 1771 analog input module updates it's data from 5 mS/8 channels (1771-IFF)to as much as 500 mS (1771-IL).

Even assuming that you could get fresh data that frequently in the CPU, you won't get it transferred to the Panelview that fast, so if your intent is to make the PV behave like an oscilloscope, you'll be disappointed.

If you still want to proceed, your strategy should be to store the value from the analog channel at the fastest practical rate in a sequence of N-registers using a FIFO or Shift Register type of instruction. Then work out a ladder logic sequence to unload the values from the stack into a destination register that the PV monitors. Use the trend object in the PV to display the data. I'm not an expert in the use of the PV, so I'm not sure what tools you have available to upate a PV's trend chart. I'd expect to see timed and change-of-state.
 
Thanks Steve this is the kind of information i am looking for. Would rsveiw 32 work to display the graph assuming I can get the plc5 to record it in time
 
If you really need updates that fast you are trying to use the wrong tool for the job. You should probably be looking at a digital oscilloscope or National Instruments Labview software plus a high speed Data Acquisition card.

Are you sure your pressure transmitter is going to have that kind of response?
 
They used the transducer to get a graph on a visitrack system. So I have been told. I am looking for a high speed plc just to track this one input. I may have to send it to a pc to monitor the graph. Thanks for the feedback.
 

Similar Topics

I swapped out a 1771 ofe1 with a 1771 ofe2/b. Got the config in and the btw/btr rslogix created. I am having an issue with the scaling registers...
Replies
8
Views
2,080
Hello everyone, My colleague and I have encountered an odd situation. We noted that, according to the historian trends, the bits in a particular...
Replies
10
Views
2,417
I need to make a PLC5/20E communicate over Ethernet with an ML1100. I have the option to place the MSG in either PLC but I can't get either side...
Replies
2
Views
2,372
Hello everybody, I have to display a message on panelview 1200 from plc5/20E when a digital input changes its state. The message has to appear...
Replies
2
Views
3,387
Hi guys, I've a strange request here; 1) Can the ethernet port of the L20E CPU use as programming port? How can this 15 pins connector be...
Replies
7
Views
6,015
Back
Top Bottom