Hello,

Can anybody advise as to the pinouts so that I may make up a lead to connect a Mitsi E300 hmi to an S7 200 (cpu226)?

Any help greatly appreciated. Thanks in advance.
 
Hi Gruntstripe,

If you click on Help -> Controller Help (in E-Designer) then a help-file will open. This helpfile contains information about addressing, cables, troubleshooting etc. You have three different possibilites:
1. Buy a CAB8 (= RS422 -> RS485 converter) and create a cable according to the drawing in the helpfile.
2. Buy a standard cable CAB20 (you can buy this cable directly from Mitsubishi, it contains circuits that converts RS422 -> RS485).
3. Buy a Siemens PC/PPI cable 6ES7 901-3BF00 and create a cable according to the drawing in the helpfile (the constructed cable is connected to the PC-side of the PC/PPI-cable).

Let us know if you need more help!

//Supporter
 
Last edited:
Hello Supporter,

I wish to avoid buying anything if I can. Not much cash you see. Previously I've made leads to connect E300 to Fx (25W to 25W D-type) and to FX0 (25W to 8W mini-din) plcs and they worked fine.

So for E300 to S7 a 25W (E300/RS422 side) to 9W (S7 RS?) lead is what I wish to construct.

I tried looking in E-Designer help but could find no info about leads (E-Designer V 6.01 build 69).

Does there have to be some kind of electronics in the lead for signal conversion or is it just passive.

Thanks.
 
Hi,

The thing is that the PPI port of the PLC communicates using RS485. Since an E300 only have 2 ports (a RS232 and a RS422-port) you will need to use a converter (either RS232 -> RS485 or RS422 -> RS485). Both CAB8 and CAB20 contains circuits/electronics that converts the RS422-signals to RS485. The PC/PPI adapter contains circuits that converts RS232 -> RS485. One way or another you will need to buy either a "ready" cable from Mitsubishi or buy a RS232/RS422 -> RS485-converter and then construct a cable between the converter and the PLC.

Let me know if you need more help!

//Supporter
 

Similar Topics

Hi, I'm using E300 as E3 Plus in emulation mode. E300 is Rockwell Automation's overload relay. But I get hardware fault when I enable Ground...
Replies
0
Views
451
When E300 powered off, the ethernet device tag data stayed at last know state, for example, fault bit is still Off, ready bit is still ON, status...
Replies
8
Views
985
Hi everyone, I have So many E300 Control module kept dead due to Module status fault. I am trying to flash them to higher version from lower...
Replies
0
Views
386
Hello, How do I go about adding an e300 to a motor greater than 200A. I have no problem adding it to any other motor less than that. Thanks!
Replies
2
Views
1,086
Hello everyone. I have a bunch of e300s connected to a startix which is then going to the plc. All of them are showing their MS and NS lights...
Replies
12
Views
4,416
Back
Top Bottom