s7 226 pid

What i could find, hope it helps.

Eight PID instructions can be used in a program. If two or more PID instructions are used with the same

loop number (even if they have different table addresses), the PID calculations will interfere with oneanother and the output will be unpredictable
 
Thanks for the reply. I thought you could have more PID loops, but the software would only support 8. I haven't programmed that many in s7-200 software, but are presses have an open loop drying system now and the the higher up would like to have a closed loop system. With that said I would need 12 PID loops.
 
Sorry as far as I know, 8 is the limit. Unless you connect one more cpu via ppi? But this will not be a popular suggestion.
 