Proworx32 help needed.

Sliver

Member
Join Date
Feb 2004
Location
Kingston, Ontario
Posts
488
New to Proworx32.
I am trying to configure a new project.
It is for an old 984-680 in a 7 slot primary rack.
I do offline setup and it accepts the 984-680 controller selection.
I try to do traffic cop but it comes up with S908 (remote I/O)
and drop 1.
I try to do an online configuration and it communicates ok(modbus)
It reads the controller properly.
I try to do the traffic cop but I get the S908/drop 1
I don't have S908 just the primary rack.
Any ideas how to configure my traffic cop?
What am I missing?

thanks,
Brian.
 
Found it...in case any others have the same problem keep S908 even when using the local drop and doubleclick on the drop. It pulls up a hightlighted area that has a box "Drop Series". To the right is a blank blue box that you click to drop down a selection with only one option "800 series". select 800 series and away you go. Not quite intuitive but now I know.

thanks,
Brian.
 

Similar Topics

We just transferred a ProWORX32 license to a new desktop. After which we transferred back ups of all the projects.PWX files to the new desktop...
Replies
1
Views
372
I was taught to go to Combined > Make Change > go to Offline > will prompt to save > Save > Exit out of program > will prompt to save again >...
Replies
0
Views
663
I'm trying to use proworx32 for the first time and can't seem to insert a vertical short between blocks. When using the [| Short] button from the...
Replies
0
Views
1,039
It's been so long since I've been inside of Modicon. Hope you can refresh my memory. Is it required to declare specific 400,000 addresses as...
Replies
3
Views
1,494
Dear Friends, I have Schneider PLC which is the world's first one Modicon i need software of Modicon PLC 984,it is known as...
Replies
0
Views
953
Back
Top Bottom