Hi,

I have been asked to write a procedure for commissioning PLC code, both new and changes to existing.
I have a few ideas, but I'm sure this must already exist in many places.
Can you help?
Do you already have a procedure for commissioning?
I would appreciate any documents you may have to speed this process along.

Thanks
 
Hi,
I don't have any writed procedure, but 1'st of all hardware must be checked. I/O-test and field devices must lines as photocells, proximityes sensing ranges between actuators distance from switces etc. VFDs settings, OL-relay settings, motor connections as Y/D between main voltage...
Emergency stop and safety circuits must work correctly.

HMI-check, all variables, Interlocks for man/auto-mode.
After that I start manual-mode operations check and then auto.
 
Winkler,

It occurs to me that the solution to your dilemma must be relative to who is asking for the procedure. For instance:

If this intended for a system like ISO9000, your answer might simply take the form of "say what you do and do what you say." By this, I mean that, 1) prior to the writing of any code, detailed documentation is generated stating the precise expectations of the new code. Then, 2) during the planning stage of the code, a check-list is submitted and approved detailing how the code is be verified (for example "With Machine in full Idle condition, push Start Button - Driven Roller A accelerates from 0 to 100 RPM"). 3) The code is then written and 4) the code is tested as per the check-list.

If, however, you are a machine builder and are looking to generally detail how the code will work for the customer, you will probably need the most detailed quote for the specific machine and develop a "do-this-and-expect-that" list. Rarely have I seen a customer actually wanting supplier to do "code" specific commissioning. Usually, the system as a whole is commissioned with the PLC code being nothing more than an internal component.

Finally, you could be looking at this from purely a machine builder's / programmer's vantage. If that is the case, I am not too sure any prewritten procedure will do much good. About all I can suggest is that you document each "thing" the new code should do, write a check-list of these things and then, during commissioning, demonstrate that it does them all.

With respect to hardware and the sequence of checking things out, I think seppoalanen's response is right on the mark.

Steve
 

Similar Topics

GitHub Link: Open Industry Project This is a side project I've been working on for some time. The goal is to provide an open platform for...
Replies
0
Views
63
Dear All, Currently i'm working with Endress Hauser flowmeter and AB PLC and try to integrate with 2 items. Flow meter spec using is Promass...
Replies
3
Views
71
Can I connect two A-B Panel View 7 to a A-B PLC. Same graphics etc. One on the local control panel and the other Panel View 7 in a remote control...
Replies
2
Views
50
Hello, I'm working with Studio 5000 and ME Station, and I'm trying to find a way to detect if the PC with the HMI is shut down or not. I've tried...
Replies
5
Views
138
Hi all smart and knowledgeable people.I have a hmi connected to 2 Plcs via ethernet.These 2 Plcs connected to control 2 systems in one machine...
Replies
2
Views
109
Back
Top Bottom