Modbus for SLC5/03

svn

Member
Join Date
Jul 2004
Posts
74
In one application, the user wants to connect their DCS with Modbus RTU on RS485 to SLC 5/03. I think SLC5/03 natively supports only DF1 or DH485. What will be the cheaper and more reliable solution in this case - using a DH485/Modbus gateway or using the Prosoft MVI46-MCM Module? or are there any other options?

Thanks

SVN
 
ProSoft’s 3150-MCM module, able to directly connect Allen-Bradley’s SLC for modbus communication will be best option
 
Thanks rPraveenkum,

I downloaded the 3100 3150 User Manual also. I shall go through the manual but mean time can you just tell me the major differences between this module and MVI46-MCM?

SVN
 
Thanks rPraveenkum for the link

BTW has anybody used DL3500 DH485/Modbus Link? How is it?


SVN
 
rPraveenkum said:
DL3500 is a DH+ to Modbus protocol Convertor

But in the DL3500-dh-385-modbus Application Note , DataLink have mentioned that it can be used for DH485 also if DH485 Commands in PLC5 format are used with SLCs, Micrologix etc. Does SLC5/03 not support these commands?

SVN
 

Similar Topics

We have a SLC5/05 that's acting as the main MTU for our SCADA system. I need to bring in some data from an AutomationDirect CLICK PLC that...
Replies
8
Views
3,423
After viewing the posts of others and helping whenever I could, it's time for me to post a topic and get some free advice. But then again, you get...
Replies
4
Views
8,479
I have a PH meter that I am trying to bring its data into 1756-L81. I have downloaded the Rockwell MODBUS AOI kit, but I am not sure if I need to...
Replies
4
Views
81
Dear All, i am trying to connect Danfoss inverter with s7 200 cpu 226.but microwin shows following error at DATA Ptr.i assigned different VB...
Replies
1
Views
42
I'm trying to control a device via MODBUS RTU and the ModbusRtuMasterV2_PcCOM in Twincat 3. I've configured a device with the right com port and...
Replies
6
Views
143
Back
Top Bottom