awendte Member A Join Date Sep 2006 Location Missouri Posts 3 Sep 11, 2006 #1 How can I view the available status bits for RSLogix5000. E.g. S:FS = First scan.
TJS Member Join Date Oct 2004 Location Ohio, US Posts 25 Sep 11, 2006 #2 You need to use the GSV function "get system value" and move them into a tag manually then take the bits you want from the structure. See sample programs for some pointers.
You need to use the GSV function "get system value" and move them into a tag manually then take the bits you want from the structure. See sample programs for some pointers.
kamenges Member K Join Date Nov 2002 Location Green Bay, WI Posts 4,332 Sep 11, 2006 #3 Check out the beginning of Chapter 14 of this manual: http://literature.rockwellautomation.com/idc/groups/literature/documents/pm/1756-pm001_-en-p.pdf That should have what you are looking for. Keith