Adding Thermocouples

dajohn6

Member
Join Date
Sep 2006
Location
Georgia
Posts
21
Hello, I'm need to add four tc to a steam dryer that had an existing tc in it. I'm using j type tc and I'm putting them through a ab-nt4 tc module that is in a slc 5/04. All I want to do is read the actual temp for now, but i am going to use it for full automation later. I'm using a panel view 600(touchscreen only) to read the temp. The problem I have is I can't get them to read correct temp. I should be in the 300 degree F, but I am reading around -800 degrees. I'm using an existing program to read the temps that has SCP (scale w/parameters) math instruction for the first rung and the second rung has a equal comparison as the input and move for my output. Has anybody seen this before?

Darren
 
Sound like a polarity problem. I would also check card configuration,
"C" or "F" and data format ( engineering units will give you
temperature, directly)

NT4.jpg



http://www.omega.com/techref/thermcolorcodes.html
 
Last edited:
Thanks For the tips. I tried reversing polarity and checked config of the channels and also I did a auto calibrate without any success. Any other help with this problem would be greatly appreciated.

Darren
 
Darren,

You didn't say how much experience you have with these, so I'll share some of the things I've learned playing with thermocouples-

1. Red is always negative, and thermocouple wire connections must be extended with more thermocouple wire.

2. Check your module hardware and configuration by shorting the input terminals. It should read the local temperature.

3. I couldn't tell if the NT4 input commons are isolated from each other. If they're not, you need to use ungrounded thermocouples. I've had trouble with grounded thermocouples picking up noise on the machine (especially if VFD's are involved) and throwing your temperature way off. Remember that thermocouples are millivolt generators and a tiny ground imbalance can wreak havoc.

4. It's been a while since I've played with an NT4, but doesn't it return the actual temperature?

Joe T.
 
Yes, the NT4 returns the actual temperature - you shouldn't need to scale it if the module is set up correctly unless its set up to format for a PID. Depending on how you set up the module it will return the actual temperature in .1 degee units, that is 300 would be 30.0 degrees, or whole degree units.
 
Thanks for the info. everybody. The tc were wired in backwards. And just to answer the question about the nt4 module having isolated commons, they do.

Thanks again,
Darren Johnson
 

Similar Topics

Hi Everyone, Currently we have three plants running with Controllogix PLCs (L72, L73, L74). In each of these plants we have 2 FTView SE...
Replies
0
Views
53
Hello, Im building project with 1756-L82ES controller and 1756-IB16S card but i cant find it when trying to add the card to IO configuration...
Replies
3
Views
134
Hello, I have a pair of redundant 1756-L71 controllers rev 24. These controllers currently have produced and consumed tag interfaces to 3 other...
Replies
2
Views
157
I'm adding an IAI Gateway with 2 axes connected to it. To an ethernet network on my PLC. So, I think the math is correct on the Input and Output...
Replies
0
Views
141
Hi Folks. I am gearing up to add a 2nd identical HMI to a project. This 2nd HMI will basically be an exact clone of the 1st one. The equipment...
Replies
3
Views
256
Back
Top Bottom