Siemens AFE drive Tripping.

Wild guess - does "AFE" refer to Active Front End? I've heard that term used in connection with some drives but never used them myself.

Might this post be better on a drives forum than a PLC forum? (and sorry, no, I don't know of one).

Ken
 
Ken M said:
Wild guess - does "AFE" refer to Active Front End?

Excellent wild guess Ken!

We have 4 AFE's in service here, but, guess what, I can find my manuals for them!

I believe that F039 means that the AFE has detected an earth fault on the DC bus, I would check the DC bus for an earth fault.

If you can find no problems with the DC bus it might be the case that the IGBT's are on their way out, how old is this AFE?

Paul
 
Check your incoming power for balance with respect to ground. Ground and Ground Fault detection can be troublesome when your power is floating or the three phase supply is running with one leg grounded.
 

Similar Topics

After updating TIA selection tool I was notified that my PLC was now under "predecessor". It was not valid if the "fail-safe" operation was...
Replies
6
Views
1,947
Hi all I have a machine with loads of asi safety switches on and I/O I was looking at the OEM Program and I’m thinking that the asi safe is an...
Replies
1
Views
1,350
I have a Siemens S7-414 PLC that has, among other things, one ET200SP rack that has one safety F-I/O card (6ES7136-6BA00-0CA0) (two emergency...
Replies
2
Views
1,555
Hi guys.Can somebody explain me or give me a practical example what is the fail-safe technology/signals . For what i read it is force plant into...
Replies
4
Views
2,541
Siemens S7-300 F-safe Cpu is connected to main cpu of same characteristics. When I make software only changes in cpu, communication cpu fails...
Replies
3
Views
2,154
Back
Top Bottom