On the scan where the timer at 2,2 (40001) reaches its preset it will pass power along the top of the rung. When column 3 is solved, cell 3,2 will solve true. 3,4 will solve false (we havent scolved column 7 yet to set 00021) – guaranteeing that 00022 will not turn on this scan. The same holds at cell 4,5. When column 7 is solved then 00021 and 00020 will turn on.
The following scan, cell 1,2 will evaluate false, causing the timer to reset when the second column is solved. It is important to remember that in the bit table bits 00021 and 00020 are still set. They will remain set until column 7 of the network is scanned. Thus when cell 3,4 and cell 4,5 are solved, the solver checks the bit table, sees that bit 00021 is still on, and solves those cells as true. Coils 00022 and 00023 will be set on. Now when column 7 is finally solved, bit 00021 will be reset.
On the next scan cells 3,4 and 4,5 will solve false.
Bits 00022 and 00023 are on for one scan only on the falling edge of the timer enable.