Hi evrebody! I got new project with Mitsubishi FX1n(but could be 2N) and load cell...now looking for anolog.to digit. converter.
Scaling range is 0-66lb +/- 0.002lb. Planning to use FX2N-4AD A/D converter which hase max.resolution of 12bits.Anlog range of
-10to10 V DC (Resol. 5v ) or -20 to 20mA. I have no experience with load cells .Could you tell me if it is right choose?
 
Your scaling resolution is going to cause problems. You state that the full range of the load cells needs to be 0 - 66lb, with 0.002Lb of resolution? That translates to 66lb/0.002 = 30,000 increments. 12 bits of analog resolution will only give you 2048 increments, therefore , for a 66lb load cell range, the smallest unit of measurement will be 66/2048 = 0.032 lbs of increments, more than 10 times the resolution you require.

Ian
 
Thank you! What is goinig to be the max. unit? And what would you advise for this scaling resolution?
Thanks again!
 
karlag said:
Thank you! What is goinig to be the max. unit? And what would you advise for this scaling resolution?
Thanks again!

What is the application?
Is this a hopper with 3 suspended S- Beam style loadcells, or a small platform scale?

There are some basic questions that need to be answered such as:
- total live weight, the displayed weight range to be measured
- total dead weight, the weight of all pieces of equipment that are part of the scale
- type of accuracy required
- Legal for Trade application

To determine system resolution, you need to know the total capacities of all load cells, then divide the total by 4000 counts. That is a typical formula we used to use at a scale company I worked at.

Any good off the shelf load cell transmitter can give you a load cell to 4-20ma output signal, but if the scale application is wrong, it does not matter how accurate your transmitter and PLC inputs are.

Ian
 
This is going to be inline mixer...amount of choped rubber ,glue and water hase to be scaled(max 7lb...min 0.01lb) not in the same time,after it all mixing and scaling again(from 7lb up to 66lb) I am in the very beginig of project and do not know what kind of loadcells I need....
Thank you again.I really apprishiate!
 
karlag said:
This is going to be inline mixer...amount of choped rubber ,glue and water hase to be scaled(max 7lb...min 0.01lb) not in the same time,after it all mixing and scaling again(from 7lb up to 66lb) I am in the very beginig of project and do not know what kind of loadcells I need....
Thank you again.I really apprishiate!

Are the ingredients to be weighed in a holding hopper then dumped into the mixer or are to be weighed into the mixer itself ?

In order to determine what load cell type and capacities to use, first you have to determine the scale application.

From experience, to weigh micro ingredients such as your application, it is always wise to weigh up in a hopper, then dump into the mixer.

Ian
 
Researched a job last year and hit then 12bit problem for the PLC analogue input. I found that instead of a converter going to an analogue signal I could get one that gave out RS232/485 information, the advantage being that the converter was 24 bit. I can't find my bookmark list for the job but found this http://www.mantracourt.co.uk/products/Amplifiers_Digitisers/DSC
with a quick Google. I don't know if it would have worked because the project didn't go ahead. Also I seem to remember in discussion with various load cell supplier that the accuracy of the load cell would be an issue. Not forgetting that you then have to program to read data from the PLC comms port.

Bryan
 
BryanG said:
Researched a job last year and hit then 12bit problem for the PLC analogue input. I found that instead of a converter going to an analogue signal I could get one that gave out RS232/485 information, the advantage being that the converter was 24 bit. I can't find my bookmark list for the job but found this http://www.mantracourt.co.uk/products/Amplifiers_Digitisers/DSC
with a quick Google. I don't know if it would have worked because the project didn't go ahead. Also I seem to remember in discussion with various load cell supplier that the accuracy of the load cell would be an issue. Not forgetting that you then have to program to read data from the PLC comms port.

Bryan

Serial Comms is always our preferred method of interfacing to weigh scales. There is no resolution lost and the problem of the weigh module display and the PLC converted weight display not matching is elimintaed.
We use Toledo Panthers with RIO on all AB applications. Only down side is the cost of each indicator and the comms module 1756-DHRIO or 1747-SN

Ian
 

Similar Topics

I am running CCW 13 trying to upload to a micro 820 vers.12 I get an output message OPC server is unable to load project controller. Please help!
Replies
1
Views
103
Hey guys, I have to take an upload of a program on an S71200 PLC to change a hardware config option and then redownload the program with this...
Replies
3
Views
99
Please help me How to B&R 7CP476.60-1 upload program Backup and download which program should I use. Pvi transfer tool.? And how. Thank you
Replies
0
Views
73
I HAVE A OLD MESSUNG HMI AND I WANT TO UPLOAD A PROGRAM FILE FROM IT TO A USB PENDRIVE WITHOUT USING PC OR SOFTWARE...WHAT SETTINGS I HAVE TO DO...
Replies
2
Views
68
in our old machine we used beijer cimrex 41 need to take program backup. i tried it with information designer software through ethernet. ip...
Replies
3
Views
73
Back
Top Bottom