Hi
I am working on Siemens Fail safe CPU.
when i download the program, Cpu Stops by the result of F_TESTC FB.
In Diag. buffer it tells that cause of stop is F_TestC.
Can anybody help me how i can know what is main reason?

Regards
Hooman
 
hooman said:
Hi
Cpu Stops by the result of F_TESTC FB.

Is this FB (Function Block) present in the CPU?

I am assuming that this FB is being called in the program, but it doesn't exist in the PLC.

Can you post exactly what the diagnostics buffer states, or maybe post a screen shot.

Paul
 
Here's what the help says: (this can be found by clicking on help on event from the diagnostic buffer display)

Safety Program: Error detected in F_TESTC

Explanation:
The F-FB F_TESTC is used to check whether the background self-tests for the F-CPU were performed fully and without error. If an error is detected, F_ TESTC either shuts down the F-runtime group within the OX3x or the entire Safety Program (fully or selectively, depending on the parameters of the FULL_SD input in the F_SHUTDN FB).
This event contains the instance DB number in F-FB F_ TEST that detected the error.



Possible Causes of Error:

Error in one of the F-CPU background self-tests
Illegal online manipulation of the Safety Program.
Internal RAM or F-CPU failure


To Correct the Error:

1. Check whether the background self-tests in the F-CPU were shut off by SFC90 H_CTRL. These tests must not be shut off.

2. Check that the F-CPU text-cycle time was set at < 12 hours in the CPU "H Parameter" properties.

or

· Restart the shut-off logic.

· Shut off the CPU and perform a cold restart.

· Perform a complete download of the user program to the CPU.

· Replace the CPU.
 
Dear Simon
Thank you very much for your Reply.
This is second Event of my Diag. Buffer.
****************************************************************
Event 2 of 120: Event ID 16# 457F
STOP caused by STOP command
Breakpoint in user program: Cyclic interrupt OB (OB 35)
Priority class: 12
FB number: 399
Module address: 1712
Previous operating mode: RUN
Requested operating mode: STOP (internal)
Event occurred in the master CPU in rack 0
Internal error, Incoming event
03:02:22:380 pm 08/04/94
***************************************************************

Best Regards
Hooman Jahanbani
 

Similar Topics

How fail safe mode in level transmitter works? customer requesting for fail safe mode when the transmitter got any issue or power loss on the...
Replies
4
Views
978
After updating TIA selection tool I was notified that my PLC was now under "predecessor". It was not valid if the "fail-safe" operation was...
Replies
6
Views
1,947
My employer is in the habit of applying a roller limit switch on a P&F chain overload in a non-fail-safe manner. The LS is only operated if the...
Replies
5
Views
1,353
I read the WinMOD manual that simulate fail-safe IO is possible with A756. But actual not, here is my configuration, anyone successes with...
Replies
0
Views
1,508
Hi guys.Can somebody explain me or give me a practical example what is the fail-safe technology/signals . For what i read it is force plant into...
Replies
4
Views
2,541
Back
Top Bottom