I am trying to monitor a Telemechanique Twido PLC with Intellution. Does anyone know how the physical digital and analog points are addressed over Modbus?

Thanks,
Charles
 
I believe the only accesible addresses in the Twido are memory words %MW (4xxxx) and memory bits %M (0xxxx)
 
You have to set the serial port to Modbus, then set the slave ID, baud rate, etc., which I am sure that you have already done. If you are using the built-in serial port (1), then you wire the Modbus signal to pins 1 & 2, and you have to jumper pins 5 & 7 as well. %MW are 4x registers with an offset of 1 (%MW0 = 40001), and %M are 0x registers with the same offset. I have been told in order to request the value of a variable, that variable or one higher must be referenced in the program. I usually accomplish this by having an operate block that might read %MW500:=100, just so that the variables up to 40501 will be valid (of course, the value of 100 for 40501 does not mean anything other than the communication is working, if you can see it on the other end). Hope this helps.
 

Similar Topics

Guys, Can please explain or show me where to find the Modbus addressing for the physical I/O (base and expansion) and the internal bits of the...
Replies
1
Views
5,617
Hello everybody, My name is Emanuel Moura, I'm from Brazil (it means, my english is not very good). I'm working with a project with PLC Twido...
Replies
4
Views
2,740
Hello, I am not new to PLC's but I am new to Twido. I am using Twido Suite 2.20.11 with a TWDLCAE40DRF. I cannot find a resource that explains...
Replies
3
Views
4,266
Dear friends i have used modbus RTU for twido. I have used the following register mapping. modbus 4xxxx --- twido %MWx modbus 0xxxx --...
Replies
2
Views
3,478
Dear all I am talking about twido and modbus. In a program I find that Twido serial port (RS485) address is 1 & the address of...