compactLogix PLC & Magelis XBT P

wce4

Member
Join Date
Oct 2006
Location
Fl.
Posts
4
Is it possible to program Magelis XBT P022010 HMI to be used with
a compactLogix PLC ? I am using V4.48 XBT-L1000 to program the HMI with the protocol ABDF1 and having no luck. Also tried AB DH5 protocal and no luck. Any help would be appreciated.


Thank you in advance.
WCE4
 
I have never used this HMI but you say it will do DF1 protocol. Before we get into baud rates, cabling and such, are you sure it can handle the Compactlogix symbolic tags? You might try mapping a SLC/PLC tag and addressing them that way from the HMI. If that doesn't work then we will look at your configuration and physical media
 
TWControls said:
I have never used this HMI but you say it will do DF1 protocol. Before we get into baud rates, cabling and such, are you sure it can handle the Compactlogix symbolic tags? You might try mapping a SLC/PLC tag and addressing them that way from the HMI. If that doesn't work then we will look at your configuration and physical media
I have Tried Maping the tags in RSLOgix 5000 it looks like this


_______Map PLC/SLC Messages________

PLC 3,5 / SLC Maping

File Nummber 11 Tag Name Test 1

____________________________________________

_____________XBT_L1000 Feild _______________

Associated Variable

File No (f): 11 i: 0
Nf:i

Equipment MASTER


Format

Object: Word
Type: Decimal
_________________________________________________

Not Woking yet time is runing out
Thank You for your Reply
 
Last edited:
Ok, also looks like it should work with Compactlogix. Do you have a like to the Magelis operating manual. I'm having a little trouble finding it. What is your communications setup on the Magelis and Compactlogix. What cable you using?
 
TWControls said:
Ok, also looks like it should work with Compactlogix. Do you have a like to the Magelis operating manual. I'm having a little trouble finding it. What is your communications setup on the Magelis and Compactlogix. What cable you using?
Communications setup on the Magelis when set to (AB DF1) Com. light does not flash. But when protocol is set to (AB DH485) com. light flashes but when I tried to send a variable to write to the PLC the HMI after a few seconds responds with impossible to write variable in PLC.Magelis operating manual can be found at http://ecatalog.squared.com/techlib/browse.cfm?hid=0b008926800cd2ab

Thank You
 
The Answer to my Question is yes but you have to set the Magelis HMI
protocol to PLC-5 not SLC-500 Thank you TWControls for trying to help me
WCE4
 
hello guys
I`m using the XBT-L1000 software but this do not have the protocol of AB.

Do you know where can I download the protocols for AB (DF1 DH-485)?


help pls
 

Similar Topics

Hi everyone, i have a compact logic 1769-L18 PLC and I'm using FTalk View ME for the display. I wanted to do some visualization on Grafana. At...
Replies
1
Views
82
Hello. Was just curious, if it is possible to load an image from an SD card on to a Compactlogix PLC that came straight out of the box brand new...
Replies
4
Views
538
I'm working on troubleshooting a PLC for a piece of manufacturing equipment. The issue I'm trying to resolve is an open wire fault not getting...
Replies
2
Views
517
Hi all, this is my first post and appreciate your advise in advance. I have a job to migrate a system form Mitsubishi FX5U to AB...
Replies
2
Views
828
Hello Everyone, A very important question: We are having trouble receiving analog output cards (5069-OF4) for our CompactLogix PLC racks. I am...
Replies
12
Views
3,175
Back
Top Bottom