When sending an Ethernet message with a Control Logix processor using the MSG instruction should the enable rung be a one shot? I'm sending a string 37 characters in length.
 
Not necessarily. Usually they're conditioned with what ever logic should cause the message, in series with "XIO MSGx.EN".

In this manner the XIO MSGx.EN (read as "message x not enabled") bit basically acts as a oneshot. Once the MSG has been scanned as true, it will be que'd and the EN bit will stay set until it gets DoNe or ERrors.

If your logic stays true for a duration, but you only want one message per false to true transition, then use a oneshot.
If you leave the message rung true, with out the conditions, the controller will know it already enabled that message and won't keep doing it, however it may use a little more scan time figuring that out. Now, if the rung goes false and true multiple times, you will get multiple messages.
At least that's been my somewhat limited experience with them. Hopefully, an expert can confirm or correct me on this.
 
Well I'm not an Ethernet/IP guru but I concur with OkiePC.

But one other question, what are your trying to communicate with?
 
I’m communicating with a PC.

I guess what I really want to know is, if the MSG is enabled does it try to complete the message until it is done or the timeout is meet even if the rung has transitioned to false.

If the MSG was enabled using a one shot will I see the .ER bit if the message fails?
 
Last edited:
If you fire the message off of a bit that you toggle it will execute once and set the DN bit when completed or the error bit if something goes wrong. No ONS is needed

If you want to continuously execute the message then you use the XIO the enable as mentioned before. The only problem with doing this is the error bit, ERR code, and ExERR code are hard to catch. I do this to get the error bits if continuously executing
PCMessage.JPG


BTW, what do you have on the PC end to communicate with the Controllogix?
 
Very good points made by both posters.

The MSG instruction executes once on a false-to-true transition of the rung. Using the XIO MessageControl.EN bit is a good practice, as is the error trap.

I don't like to continuously execute messages, both to save bandwidth and to avoid any possible problems in the Logix execution queue. There was a bug back in v6 or so in which an operating MSG instruction that had not completed would prevent the controller from entering Program mode, and I never abandoned that practice.

If I have an I/O connection also to the device I'm sending the MSG instruction to, I execute a GSV to determine the status of the connection before I execute the MSG, so I avoid trying to make a connection to a device that might be disconnected from the network.

Another very common practice in ControlLogix is to manually set the .TO timeout bit in the control word after a MSG instruction has been enabled but not completed or errored for a period of time. Unlike the SLC/PLC5 MSG instruction, there's no native timeout in the message instruction itself, so it depends on the link layer to provide a connection error if the message can't get through.
 
I don't even address the error bit in my program. I used the ERR code and ExERR code to display a fault message associated with the particular code on a display. Much better then just saying the message is broke
 
I do use the .ER bit to display a comm fault for the specific device I’m trying to communicate with, it is just used as a generic comm fault. The .ERR would be a more specific fault indication.



Thanks again for the replies.
 

Similar Topics

Does anybody have experience with a Bruker Optics FT-NIR and transmitting quant results to a PLC via Ethernet/IP? I am going to interface this...
Replies
2
Views
1,707
Hello I have a s7-1200 and I would like to read the tags present in this controller with my controllogix controller. The two controllers don't use...
Replies
3
Views
37
Can we use a Simotion D455 ethernet port x127 as a gate, to access S7-1500 plc Tia Portal program ? In the Simatic manager, we used Netpro to do...
Replies
2
Views
82
So I have a sort of unique situation where I'm wanting to run a PF755 from the IO and over ethernet. Of course, this comes with it's own set of...
Replies
9
Views
259
Hi all, My ethernet port on my laptop recently broke and I was hoping to just use a usb-c dongle in the mean time to go live on my PLC until I...
Replies
14
Views
453
Back
Top Bottom