Russ
Lifetime Supporting Member
A few days ago I was checking the signal strength on a fire-eye module. The range was 4.00-5.50VDC, and the reading was a solid 5.2X range.
When I went to place the cover back on I accidentally pressed the 'reset' button.
NORMALLY this just shuts down both burners (there are 2 burners per actuator). Normally I just reset the plc and relite. Thirty seconds and it's done.
But.. this time.. the 'flame detected' light stayed on... on BOTH BURNERS!!! I reset the alarm, and it would come right back. I swapped the amp cards. Once inserted the flame detected light came on. I put a meter to the amp card again.. this time they read between 4.70-5.09VDC, which is really strong.. considering that the burners were supposed to be off at this time.
I thought that maybe the uv scanners had possibly 'burned in'. They're the old style (shutter-less).
However when I went to the burner I found flame. Both burners still had flame visible from the site ports. Both maxon gas valves (there are 2 in the train) were 'shut' according to the window. I tapped one of the pilot solenoids, and nothing happened.
I then shut a manual valve that was between the two maxon valves and both burners went out.
It appears that gas was passing through both 'shut' valves.
Tomorrow, when the plant has time, I'm going to clean both valve seats. My first thought is that there is build-up on the seats. This, coupled with the draft fan running at 57Hz creating a nice negative static at the burners, is why I believe that the burners stayed lit after 'shut down.'
Would like some feedback, and also some other things that might be good to look at. I'm also thinking about the springs. Maybe they need to be replaced?
These actuators have been in service since 1989. I don't believe the valve seats have ever been cleaned.
When I went to place the cover back on I accidentally pressed the 'reset' button.
NORMALLY this just shuts down both burners (there are 2 burners per actuator). Normally I just reset the plc and relite. Thirty seconds and it's done.
But.. this time.. the 'flame detected' light stayed on... on BOTH BURNERS!!! I reset the alarm, and it would come right back. I swapped the amp cards. Once inserted the flame detected light came on. I put a meter to the amp card again.. this time they read between 4.70-5.09VDC, which is really strong.. considering that the burners were supposed to be off at this time.
I thought that maybe the uv scanners had possibly 'burned in'. They're the old style (shutter-less).
However when I went to the burner I found flame. Both burners still had flame visible from the site ports. Both maxon gas valves (there are 2 in the train) were 'shut' according to the window. I tapped one of the pilot solenoids, and nothing happened.
I then shut a manual valve that was between the two maxon valves and both burners went out.
It appears that gas was passing through both 'shut' valves.
Tomorrow, when the plant has time, I'm going to clean both valve seats. My first thought is that there is build-up on the seats. This, coupled with the draft fan running at 57Hz creating a nice negative static at the burners, is why I believe that the burners stayed lit after 'shut down.'
Would like some feedback, and also some other things that might be good to look at. I'm also thinking about the springs. Maybe they need to be replaced?
These actuators have been in service since 1989. I don't believe the valve seats have ever been cleaned.