Greetings bundhit ...
sorry that I’m short on time ... but as near as I can tell from here, these should be the DIP switch settings for your two ASB modules ...
the ones that I’ve highlighted are the ones that I think you’ll need to change ... but ... I might be reading your original post wrong too ... if it appears that might be the case, please post again and give us more details as to your present switch settings ...
also ... you haven’t mentioned how you have the “G-Data” configured for your SN module ... I think (again based on how I understand what you’ve posted) that the following setup is what you need ...
on another note: if all three chassis are located close enough together in the same enclosure, then there is a chance that you don’t need the expensive SN module and/or the two ASB modules at all ... have you researched the possibility of using the 1746-C7; 1746-C9; or 1746-C16 “chassis interconnect cables” for your system? ... the different part numbers are for different cable lengths ... the longest is about 50 inches long ... be sure that you understand how to connect the chassis end-to-end correctly if you decide to go this route ... if this will work for you, it could save about $2,000 or more - and make addressing and troubleshooting the system a LOT easier in the long run ...
one more thing - from your latest post ...
when you use a 1747-ASB module, the numbering of the slots in the chassis changes ... “Slot 0” will not contain the ASB ... specifically, the ASB slot will not have a number assigned to it ...
hope this helps ...