I am looking to control position with of an indexer that will normally have 3 desired positions 0% 50% and 100% (SP).
PV: 4to20 position encoder (scaled 0-1000)
SP: Varie from 0 to 100% ,100% to 0, 0 to 50% or 50% to 100%
OUTPUT: Propotionnal valve (4to20)
Must I filter the setpoint, because the setpoint jumps from 0 to 100... It is not progressively going up 0-5-10-15....
Must I use the controller in cascade ? (the setpoints will be coming from the remote set point parameter)
Can anyone confirm the parameters I set:
PID LOOP 1 TITLE: POSMTR REMOTE SETPOINT: V526
CLAMP SP LIMITS: LOW = +0.00000
POS/VEL PID ALGORITHM: POS HIGH = +1000.0
LOOP VFLAG ADDRESS: C4250
SAMPLE RATE (SECS): +0.30000 LOOP GAIN: +1.00000
RESET (INTEGRAL TIME): +0.50000
PROCESS VARIABLE ADDRESS: V525 RATE (DERIVATIVE TIME): +0.00000
PV RANGE: LOW = +0.00000 FREEZE BIAS: NO
HIGH = +1000.00
DERIVATIVE GAIN LIMITING: NO
PV IS BIPOLAR: NO LIMITING COEFFICIENT: +10.0000
SQUARE ROOT OF PV: NO
20% OFFSET ON PV: NO SPECIAL CALCULATION ON: PV
SPECIAL FUNCTION: SFPGM1
LOOP OUTPUT ADDRESS: WY521
OUTPUT IS BIPOLAR: NO LOCK SETPOINT: NO
20% OFFSET ON OUTPUT: YES LOCK AUTO/MANUAL: NO
LOCK CASCADE: NO
RAMP/SOAK PROGRAMMED: NO
RAMP/SOAK FOR SP: NO ERROR OPERATION: NONE
REVERSE ACTING: NO
ALARM DEADBAND: +0.00000 MONITOR DEVIATION: NO
DEVIATION ALARM: YELLOW = +0.00000
MONITOR LOW-LOW/HI-HI: NO ORANGE = +0.00000
MONITOR LOW/HIGH: NO
PV ALARMS: LOW-LOW = +0.00000 MONITOR RATE OF CHANGE: NO
LOW = +0.00000 RATE OF CHANGE ALARM: +0.00000
HIGH = +1000.00
HIGH-HIGH = +1000.00 MONITOR BROKEN XMITTER: NO
PV: 4to20 position encoder (scaled 0-1000)
SP: Varie from 0 to 100% ,100% to 0, 0 to 50% or 50% to 100%
OUTPUT: Propotionnal valve (4to20)
Must I filter the setpoint, because the setpoint jumps from 0 to 100... It is not progressively going up 0-5-10-15....
Must I use the controller in cascade ? (the setpoints will be coming from the remote set point parameter)
Can anyone confirm the parameters I set:
PID LOOP 1 TITLE: POSMTR REMOTE SETPOINT: V526
CLAMP SP LIMITS: LOW = +0.00000
POS/VEL PID ALGORITHM: POS HIGH = +1000.0
LOOP VFLAG ADDRESS: C4250
SAMPLE RATE (SECS): +0.30000 LOOP GAIN: +1.00000
RESET (INTEGRAL TIME): +0.50000
PROCESS VARIABLE ADDRESS: V525 RATE (DERIVATIVE TIME): +0.00000
PV RANGE: LOW = +0.00000 FREEZE BIAS: NO
HIGH = +1000.00
DERIVATIVE GAIN LIMITING: NO
PV IS BIPOLAR: NO LIMITING COEFFICIENT: +10.0000
SQUARE ROOT OF PV: NO
20% OFFSET ON PV: NO SPECIAL CALCULATION ON: PV
SPECIAL FUNCTION: SFPGM1
LOOP OUTPUT ADDRESS: WY521
OUTPUT IS BIPOLAR: NO LOCK SETPOINT: NO
20% OFFSET ON OUTPUT: YES LOCK AUTO/MANUAL: NO
LOCK CASCADE: NO
RAMP/SOAK PROGRAMMED: NO
RAMP/SOAK FOR SP: NO ERROR OPERATION: NONE
REVERSE ACTING: NO
ALARM DEADBAND: +0.00000 MONITOR DEVIATION: NO
DEVIATION ALARM: YELLOW = +0.00000
MONITOR LOW-LOW/HI-HI: NO ORANGE = +0.00000
MONITOR LOW/HIGH: NO
PV ALARMS: LOW-LOW = +0.00000 MONITOR RATE OF CHANGE: NO
LOW = +0.00000 RATE OF CHANGE ALARM: +0.00000
HIGH = +1000.00
HIGH-HIGH = +1000.00 MONITOR BROKEN XMITTER: NO