I am using an specific IR temperature sensor device that requires basically NO bias current (they spec it in the nano amp range). Unfortunately, the IR device manufacturer didn't tell us that until after the devices (all 24) were installed and wired. Thus our accuracy is way off.

Has anyone figure out what resistor to trim to remove the bias (open circuit) current on the 1794-IT8? One of my co-workers reverse engineered the circuit until the multiplexer but thats were we "lost the trail".

Any another ideas would be appreciated as well. We are considering amplifers, or making a unity gain buffer with op amps...unfortunatley we don't have much room left to mount addition devices. Plus we are trying to control our rework costs.

Thanks,
Chad
 
More info on the sensor specs.
Have you tried grounding one side of the signal?


The 1794-IT8 is a temperature/mV measuring module that accepts inputs from a variety of thermocouples and from the mV source in the range of ±76.5 mV. Use cold-junction compensators (cat. no. 1794-CJC2) in thermocouple mode. Two cold-junction compensators are shipped with the 1794-IT8.
 
Last edited:
The spec sheet says it is type K wiring. Is the hook up wire you used
type K thermocouple wire. If not that will creat a junction at each
connection. Each connection will then act like a thermocouple and
generate a voltage. Also any crimp connectors, terminal strips,
plugs or jacks must be for type K thermocouples.
 
Yup...check all that.

We talked directly too exergen and they stated the bias current of the analog card is too high. It needs to be in the nano amp range.

CG
 

Similar Topics

Just commissioned two new skids for a customer. Each has a 1794 chassis over Ethernet back to an L81. The second module of each chassis is a...
Replies
8
Views
2,375
Hello Im using module 1794-IT8 to read values from termocouple type K. I configured the module to read this type of termocouple and i still get...
Replies
8
Views
2,360
So this is a first time I've had no choice but to use Flex I/O with anything RSLogix 5000. I've got everything up and running, but the values I...
Replies
2
Views
1,966
We are getting ready to do a small project with AB Flex I/O and intend on using a 1794-IT8 module to measure some temperatures. We are using a...
Replies
1
Views
2,354
Installing a IR T/C onto a DeviceNet Flex IO drop. Card is a thermocouple card 1794-IT8/A. According to the manufacturer, I'm getting leakage...
Replies
0
Views
1,900
Back
Top Bottom